Inducer and circulator runs

stampman
stampman Member Posts: 2
For no reason after hot water has been satisfied the circulator and inducer run for a period of time.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,859
    Many controls are setup with an off delay. Likely yours is. Removes heat from the boiler and puts it somewhere useful
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    EdTheHeaterManstampman
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,386
    Post purge to clear out combustion gasses and possible raw fuel from the boiler to the outdoors where it will pose no safety hazard. That is the combustion fan or inducer fan. That is a safety standard for some equipment. Dont worry about it.

    The circulator operating after call for heat is satisfied. Consider this: during a call for heat or DHW the boiler gets up to the limit temp of (lets say) 180°. At the end of that call for heat, the circulator stops. now you have 180° of water in the boiler that is sitting in the boiler that is in a boiler room that is not contributing to the load of the home (or the DHW tank) after one hour passes that wasted heat has now radiated into the boiler room (where no one lives) making the unused space hotter than it needs to be (if a basement, it wasted where no one needs it, if a laundry room then that room gets too hot).

    Now if you operate that circulator pump for 3 to 5 minutes, with no flame That 180° may drop to 160° making the DHW a few degrees hotter. that means there is more hot water now as a result of the "post purge" of the heated boiler water. that might make the water heater call for heat 30 minutes later than if it did not have that extra heat wasted in the boiler room.

    At the end of the year, add up all those 30 minutes of savings and you could see a noticeable difference in your fuel usage.

    I know that is one of several things that make EK boilers more efficient.

    I would not worry about it.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    stampman
  • stampman
    stampman Member Posts: 2
    Thank you very much for your responses. I guess I was worried for nothing.
    EdTheHeaterMan