Two temperature boilers plumbing circulator location
Kkane97
Member Posts: 10
I currently have a crown non condensing boiler, two zones both baseboard through my house. Iam wanting to switch one zone to radiant flooring. Doing so I am concerned about return water temperature being to low and need to add a mixing system in to regulate that and lower the temperature loop for the radiant section. I have currently 2 circ pumps in the return sides of my system, looking into plumbing designs I found one that I think will satisfy my needs and be the most simplistic to plumb in my system only using two three way mixing valves, one for the low temperature radiant and the other for regulating return water temperature. Of this design just omitting the second loops mixing valve and continuing high temperature loop. But all the diagrams I am seeing have circulator pumps on the supply sides of the radiant loops, in my application for adapting my current system it would be much simpler to me to leave them in the return side. Is there a reason I commonly see circulator pumps on supply side?

0
Comments
-
Provided you have independent pumps powering each circuit, yes you can either have the pumps on the supply (after the mixing valve) or the return, before the mixing valve.
However. Doing that you wind up with both pumps being, from the standpoint of water circulation, a long way from your expansion tank and thus being at the lowest pressure point of the loop, rather than at the constant pressure point of the expansion tank. Not good. Not good at all. Unless the overall system static pressure is enough higher to keep good pressure on those pump inlets there is a very real risk that they won't have enough intake pressure at least from time to time -- and cavitate, which destroys pumps.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Do you know the heat load of the two zones you are considering?
What about boiler size?
One rule of thumb is if the radiant is 10- 15% of the boiler output, a return protection valve probablyis not essential. The reason being the boiler can catch up top that load rather quickly.
One mixing valve for the low temperature is all you need. The other loop runs at boiler temperature.
Is the boiler on outdoor reset control?
If so and the radiant is only one zone then a manual 3 way mix valve is a simple option. its temperature output tracks along with the boiler temperature. based on outdoor reset.
A thermostatic 3 way is another option, but it stays at a fixed temperature.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Jamie Hall said:Provided you have independent pumps powering each circuit, yes you can either have the pumps on the supply (after the mixing valve) or the return, before the mixing valve. However. Doing that you wind up with both pumps being, from the standpoint of water circulation, a long way from your expansion tank and thus being at the lowest pressure point of the loop, rather than at the constant pressure point of the expansion tank. Not good. Not good at all. Unless the overall system static pressure is enough higher to keep good pressure on those pump inlets there is a very real risk that they won't have enough intake pressure at least from time to time -- and cavitate, which destroys pumps.0
-
hot_rod said:Do you know the heat load of the two zones you are considering? What about boiler size? One rule of thumb is if the radiant is 10- 15% of the boiler output, a return protection valve probablyis not essential. The reason being the boiler can catch up top that load rather quickly. One mixing valve for the low temperature is all you need. The other loop runs at boiler temperature. Is the boiler on outdoor reset control? If so and the radiant is only one zone then a manual 3 way mix valve is a simple option. its temperature output tracks along with the boiler temperature. based on outdoor reset. A thermostatic 3 way is another option, but it stays at a fixed temperature.0
-
Ask @hot_rod if this diagram is better.
it places the boiler circulator after the expansion tank and if you are lucky enough to have a built-in boiler air scoop, then adding a vent in the boiler will be an excellent place to vent dissolved air from the system. The hottest water and the lowest pressure in the system is where dissolved air will separate. If there is a vent location in the boiler casting, that is where the lowest pressure and the hottest temperature water is located.
Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics0 -
@EdTheHeaterMan that's exactly what I was thinking as far as the diagram as far as the mixing valves thank you, currently my expansion tank and air vent and filler are on the outlet of the boiler before it tees off to either zone0
-
Are you going to use the SEP4 in your repipe? @hot_rod is the expert on that stuff and may have a better or less expensive idea for you. I think he will chimes in sometime tomorrow.
Which cast iron boiler are you using? Brand & model number. We can look up if you have the built in air scoop tapping.Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics0 -
That 10K radiant load should not cause a 90K boiler to condense, so no worry about return protection.
Same with copper fin tube, it is low mass and would not generally require boiler return protection.
If I were a betting man, I'd guess the boiler is also oversized to the total building load? only a room by room calc could answer that.
Here are three options using a 3 way mix valve. The first, direct pipe assumes the boiler can operate with 1 gpm flow. Most cast iron boilers can.
Primary secondary series loop costs one more circ.
The sep is another option.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
hot_rod said:That 10K radiant load should not cause a 90K boiler to condense, so no worry about return protection. Same with copper fin tube, it is low mass and would not generally require boiler return protection. If I were a betting man, I'd guess the boiler is also oversized to the total building load? only a room by room calc could answer that. Here are three options using a 3 way mix valve. The first, direct pipe assumes the boiler can operate with 1 gpm flow. Most cast iron boilers can. Primary secondary series loop costs one more circ. The sep is another option.0
-
EdTheHeaterMan said:Lowest cost design. I would use it for one of my customers.0
-
In the future if im happy with the radiant and can provide sufficient heating as my primary source the other zone I would like to switch over to it as well as I redo parts of the house. If this is the case would it be better to have a boiler protection loop?0
-
So the 90K boiler could in fact be twice the size you need? There will be some short cycling of that sized boiler with a 10K or smaller load that the radiant demands.
A 50K condenser would be an ideal swap, someday. Especially if you go all low temperature radiant.
The direct pic that Ed shows does have circs in series, so it will be doubling the head, possibly over-pumping a bit?
Maybe a delta P circ as the boiler circ would minimize that. I think it would work okay without the boiler circ.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
I got back this evening and checked it's a crown twz100 100k btu. So sounding like it's definitely oversized, house isn't to badly insulated I redid the crawl spaces and sealed a bunch of windows up a couple years ago. As far as short cycling I don't recall it running for less than 5 minutes at a time which I know is a little low, is the radiant going to cause to to short cycle even worse than that? Lower temperature heat output over a longer duration for the radiant.
My rough numbers could be off but I agree it's definitely big it seems like, for the last two years on it I heated the whole house for about 375 gallons of fuel0 -
-
After closer look. and reading Hot Rod Bob's comment. It appears that I may have made my second mistake on HH. How could that be? This is a lower cost option:
Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics0 -
-
EdTheHeaterMan said:After closer look. and reading Hot Rod Bob's comment. It appears that I may have made my second mistake on HH. How could that be?
My simplest way to plumb in would to be leaving my circulator pump on my returns so after my radiant loop in the diagram, my circs on the return side0 -
So for now, consensus is simplest design, shouldnt be a issue for now as for as condensate, one mixing valve for the low Temp zoneKkane97 said:EdTheHeaterMan said:After closer look. and reading Hot Rod Bob's comment. It appears that I may have made my second mistake on HH. How could that be?
My simplest way to plumb in would to be leaving my circulator pump on my returns so after my radiant loop in the diagram, my circs on the return side
If it is easy enough to do it, try to put the high temp circulator pump on the supply side after the expansion tank on the supply side. like the diagram above
This would be the least friendly arrangement for air removal.
Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics0 -
You need to pump away from the mix port of a 3 way valve. This allows it to pull from the H &C port of the valveBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 84.3K THE MAIN WALL
- 2.9K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 44 Chimneys & Flues
- 1.8K Domestic Hot Water
- 4.8K Gas Heating
- 120 Geothermal
- 156 Indoor-Air Quality
- 3K Oil Heating
- 57 Pipe Deterioration
- 794 Plumbing
- 5.4K Radiant Heating
- 369 Solar
- 14.1K Strictly Steam
- 3.1K Thermostats and Controls
- 53 Water Quality
- 39 Industry Classes
- 80 Job Opportunities
- 22 Recall Announcements