No hot water / mixing valve replaced

2»

Comments

  • hot_rod
    hot_rod Member Posts: 22,703
    We have seen tankless coils cause thermostatic mixers to be inaccurate. The pressure on the hot side can sometimes be less due to a scaled coil. Whenever there is a big pressure imbalance mix valves tend to misbehave. How is the pressure on a cold faucet compared to flow with just cold, on the same faucet?

    A noticable pressure drop is another indication of a partially plugged coil. Has it ever been flushed?
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream