Replacement for old Honeywell S86H intermittent pilot control
garbid
Member Posts: 17
in Gas Heating
Can any of the "old hands" recommend a suitable replacement for my Honeywell S86H intermittent pilot with 100% shutoff and auto ignition (25v, PV & MV = 2A max., 90 sec. ignition trial)? Honeywell doesn't show a replacement in its cross reference guides and the sources I've checked list it as obsolete (with good reason: it's on a very old Burnham boiler that has worked flawlessly for decades). There's nothing wrong with it but I fear that its age, like mine, might cause it to act up in the depths of winter one of these days. (I am replacing the Aquastat as well for the same reason.) Thanks for you help.
0
Comments
-
Use the Honeywell S8610U. It can be programmed to mimic your present control.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Thanks for the suggestion, Steamhead.0
-
Steamhead: Does the Honeywell S8610U ‘s lower PV load rating of maximum 1A vs the old unit’s 2A make any difference?0
-
Shouldn't. What gas valve is on that unit? Is there a separate pilot valve?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
The gas valve is Honeywell VR 844 P 5018 (also an old one but seems to operate fine).0
-
Hellow @garbid,
As @Steamhead said above.
I can't find a specification on that Gas valve. Someone could measure the PV current to be sure.garbid said:Steamhead: Does the Honeywell S8610U ‘s lower PV load rating of maximum 1A vs the old unit’s 2A make any difference?
The gas valve is Honeywell VR 844 P 5018 (also an old one but seems to operate fine).
Honeywell document.
https://s3.amazonaws.com/s3.supplyhouse.com/manuals/1299090484970/49449_PROD_FILE.pdf
S8610U replaces
S86H1006
S86H1022
S86H1048
S86H1089
S86H1097
S86H1105
S86H1121
S86H1147
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Thanks for the information and link, 1095_A. I’ll measure the PV current as you suggested. I assume I do that from the existing pilot module to the gas control.0
-
Hello again and thanks for all of the tips. The Honeywell (Resideo) S8610U is indeed the correct replacement for my old Honeywell S86H1006 module and now I’m ready to install the new one, but I’m a bit confused as to where the old 25v(1) and 25v (2) wires connect on the new module as the installation instructions aren’t particularly clear. (There is no vent damper.). Thanks for clarification.0
-
Hello @garbid,
I suppose the only oddity here, is it to make sure the old 25v(1) or 25v (2) wires from the boiler (one or the other) were not grounded elsewhere. If so the grounded one should be connected to the 24V (GND) terminal.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Always read through your installation documents so you are familiar with the control wiring.
0 -
Thanks for your responses and helpful tips.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements