Need some advice on oils level an old semi hermetic trane compressor
RayWohlfarth
Member Posts: 2,043
We inherited a Trane Semi Hermetic from the 1960's model 2F5A68 What is the old level supposed to be in the sight glass? Thanks for your help
Ray
Ray
Ray Wohlfarth
Boiler Lessons
Boiler Lessons
Sun 3GS was probably the oil.0
@RayWohlfarth like a boiler sight glass. If you can see the oil level its safe to run.
optimum is usually half a glass as @pecmsg mentioned. The level will fluctuate if the compressor has unloaders opening and closing or multiple solenoid valves to feed multiple coils etc. Liquid tends to migrate into the oil which the CC heater is supposed to take care of, but you always get some. When the compressor starts the suction pressure and crankcase pressure drop so the liquid refrigerant in the oil flashes into vapor and drops the oil level momentarily. You can also measure the oil pressure at the pump and subtract the suction pressure from that reading to get the net oil pressure.0 -
@MikeAmann yes, I realize that now0