Two zones getting heat- only one being powered
rob51
Member Posts: 67
Hi. I recently changed out my thermostat wire in my taco 504 relay box. When I went to turn the boiler back on, DHW (which runs from the relay) and 1st floor zone heating turned on at the same time. There was no call for heat for the first floor- only DHW. Is this a stuck check valve? What are my options besides replacing the flocheck valves? Maybe something else is wrong? Thank you.
0
Comments
-
General rule. If you do something -- in this case changing out the thermostat wire -- and something which worked right before doesn't work right now, start with what was changed and go over it completely and actually verify that it is all correct. Sometimrs helpful to get another set of eyes on.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Thank you. Yes. I checked. It’s only calling for one zone of heating (the DHW). The other zone which is heating isn’t being called for according to the relay panel indicator lights.0
-
Is the misbehaving zone valve opening? If so, where is it getting power? It's possible the relay block got fried -- but I'd b very sure there isn't an odd short somewhere before starting to replace parts.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Zoned with pumps.? If so the check or flo check would be a place to look.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I figured it out. I had the thermostat wires were hooked up incorrectly. Too many wires and not enough time, if you ask me.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements