Two new videos this week The case for 2 psi and The case of the tripped limit controls

RayWohlfarth
RayWohlfarth Member Posts: 1,596
Here are the links
https://youtube.com/watch?v=CvRxCrPwFWI

This is the one for 2 psi steam pressure
https://youtube.com/watch?v=ceSfgRt0jPc
Ray Wohlfarth
Boiler Lessons
GGross

Comments

  • retiredguy
    retiredguy Member Posts: 955
    These isolation valves were added to a hot water system after I retired and boy I bet that they save a ton of money. Ha,Ha. Some engineer thought that they had just saved us from running out of fuel, what a joke. If you are going to add a component make sure that you do all the "engineering" and not just spec a device. I guess that is why we have service techs that will finish the engineering design work.
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,596
    @retiredguy I never imagined it would keep heating the way it did.
    Ray Wohlfarth
    Boiler Lessons
  • JUGHNE
    JUGHNE Member Posts: 11,180
    I had a large house with gravity piped system starting out at 2 times 3" supplies.

    A lot of heat would be retained in the piping and CI boiler when tstat shut boiler and pump down.

    Simple solution was a strap on aqua stat to hold the pump relay on until water cooled down, milking the residual heat out of basement pipes which are well insulated.

    Somewhat like your time delay but simpler.

    CLamb
  • retiredguy
    retiredguy Member Posts: 955
    Back in the 1970's when I was still doing residential heating all pumped hot water systems had the pump controlled by an aquastat set at around 110 F. Back then almost all systems were piped with steel pipe and most radiation was cast iron.The pump ran any time the systems water temp was above that setting.
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,596
    @JUGHNE That was pretty common back then and simple solution. There is lots of heat left in those cold cast iron sectional boilers. I read about a solution @DanHolohan recommended when I had my old boiler and installed a time delay relay on my burner. On a call for heat, the burner would start about 10-15 minutes after the pump and in most instances, the burner never fired.
    @retiredguy That wasn't efficiency I guess LOL
    Have a good weekend gentlemen
    Ray Wohlfarth
    Boiler Lessons
  • Steamhead
    Steamhead Member Posts: 17,167

    @JUGHNE That was pretty common back then and simple solution. There is lots of heat left in those cold cast iron sectional boilers. I read about a solution @DanHolohan recommended when I had my old boiler and installed a time delay relay on my burner. On a call for heat, the burner would start about 10-15 minutes after the pump and in most instances, the burner never fired.
    @retiredguy That wasn't efficiency I guess LOL
    Have a good weekend gentlemen

    We had this happen too. Solution there was to replace the standard aquastat relay with a Beckett AquaSmart. Besides its 2012-compliant weather-responsive ("Heat Manager") features, the AquaSmart has a circulator-off delay option of up to 4 minutes 15 seconds, which when activated, keeps the circ going long enough to move the residual heat out to the system.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • JUGHNE
    JUGHNE Member Posts: 11,180
    The old CI boiler I spoke of was burner on pump relay on....burner off, pump off.

    So pipe strap on aquastat was the simplest money.

    This was replaced with Mod Con simply because the brick chimney was defunct.
    No simple repair, liner or B vent possible or feasible.

    Over the years with the modcon, the cleanings and repairs would almost wipe out that added maybe 10% of efficiency.
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,596
    @Steamhead I have never used one of those but have looked into using one. It seems like a nice control
    @JUGHNE The mod cons do require more maintenance than a standard CI with a standing pilot. The customers dont understand that at all
    Ray Wohlfarth
    Boiler Lessons
  • jumper
    jumper Member Posts: 2,354
    Don't like to stop/start motors but heating fuel was less expensive then.
  • Steamhead
    Steamhead Member Posts: 17,167

    @Steamhead I have never used one of those but have looked into using one. It seems like a nice control

    Most of the ones that come on new boilers are Hydrolevel Hydrostats. These are also 2012-compliant, and we use them too, but they don't have the circ-off delay feature.