Davey76
Davey76 Member Posts: 1
I am the owner builder but I had an experienced plumber run my radiant lines but my crew installed the actual flooring system.  Similar to warm board but cheaper. My radiant supply manifold is the same temp as the return on 2 of my 3 manifolds.  Does that mean the supply and return loops got mixed up ?

Comments

  • Paul Pollets
    Paul Pollets Member Posts: 3,656
    Options
    Check the S&R manifold inlets with an infra red themometer. The supply should be significantly warmer. When operating correctly, there should be a 10 degree difference, depending on boiler controls and type of mixing valve used. Pump sizing also matters.
    Derheatmeister
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Options
    Could be overpumped too.

    There was an error rendering this rich post.

    mattmia2Rich_49
  • Ironman
    Ironman Member Posts: 7,376
    Options
    How about some pics?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • mattmia2
    mattmia2 Member Posts: 9,680
    Options
    Anther great question this time of year is what temp is the water and what temp is the ambient?
  • tim smith
    tim smith Member Posts: 2,752
    Options
    outdoor reset may be keeping water temps down near room temp, then no td.
    good luck
    mattmia2
  • hot_rod
    hot_rod Member Posts: 22,158
    Options
    If the room is warm or t-sat about satisfied you may not see much of a ∆.
    Are there flowmeters at the manifold?
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • GroundUp
    GroundUp Member Posts: 1,911
    Options
    Check the loops themselves, not just the blended temp. If they are mixed up, that's how you'll find out. There is also a possibility that your knockoff Warmboard isn't allowing for any heat transfer.