The Case of the Unopening Gas Valve, this weeks case
RayWohlfarth
Member Posts: 1,675
In this case, the customer had one boiler not working. My diagnosis was the one gas valve was defective. I had gas pressure before the valve and power on the valve and no gas after. After changing the gas valve with another, the problem persisted. What do you think caused the issue? I'll let you know what I found on friday morning at 6am EST
Ray Wohlfarth
Boiler Lessons
Boiler Lessons
0
Comments
-
-
I agree with @ratio although he must have gotten out of bed before me. It could also be that the adjustable gas bleed orfice was closed. (same as the first answer)0
-
Surely someone reset the low gas pressure cutoff, if present.
No voltage at valve would have shown that though.0 -
Where is pressure being tested after the valve? There's no manifold test port on the valve? Was it tested near the valve or at the end of the train?0
-
-
Vent plugged agree wit @ratio0
-
Well @ratio was the first correct answer and the gas train vent was plugged. I too have a spare valve because I missed the diagnosis. I keep it on the shelf in my office to remind me. Im glad it wasn't a 3 or 4" gas valve. At the end of the video I share the formula I use when sizing the gas train vents.
Here is the link to the video. https://youtube.com/watch?v=Eu6gj1gUQrQ
Ray Wohlfarth
Boiler Lessons1 -
The end of the vent line was plugged so tight that I ended up making an adapter from ¼ compression to ¼ flare & blowing it out with N₂. I think I ended up at around 200 psig before the cork popped.0
-
-
@ratio Thats incredible how they plug like that in a relatively short time. Never had to use that much pressure LOL
@JUGHNE Sounds like a terrible service call. I like your idea of using the USMC method LOL
Ray Wohlfarth
Boiler Lessons0 -
Bees, wasps and ants love small vents.
One reason MA specs vents mut be 3/4" IPS or larger if they exceed 40'0 -
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements