hydro level set up
tsayles50
Member Posts: 36
recently purchased a house with a hydro level auto filler. I stopped using it because it was overfilling the boiler. Any guidance on how to calibrate these things correctly?
0
Comments
-
Is it wired to a lwco?0
-
yes it is0
-
Can't say without more information. First, though, the Hydrolevel should be being tripped by the low water cutoff -- so the first thing to check is whether the low water cutoff is working properly, and, if it is not a probe type, if the connections to the boiler are free and clear.
Then assuming it is, the question is -- what model Hydrolevel? There are, I think, about 10 of them, and they're different in how they can be set and controlled...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
VXT-120. There is an overfill problem not a problem with it emptying and the autofiller not kicking in. Since I stopped using it I haven't had problems with it overfilling and it hasn't gone dry so I don't think it is a leak. Could the water level drop too low when the boiler is going and then it overfill?0
-
It may be that the diaphragm in the valve is going bad. One way to check- with the water to the feeder turned on, press the "feed" rocker switch on top of the VXT. The valve should open and water should flow. When you release the switch, the valve should close instantly- if it does not, the valve needs rebuilding.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
https://hydrolevel.com/wp-content/uploads/2021/06/VXT-120-Instructions-web-0321.pdf
See page 3 of the manual. You can remove the cover plate by loosening the two screws one on the left and one on the right side of the unit with a flathead screwdriver and check the feed amount setting.0 -
If @Steamhead 's check shows the feeder to be OK, check what the time delay and feed amount switches are set to (refer to the manual for the feeder). Improper settings for those can lead to significant overfilling.
Also, you haven't mentioned the type of low water cutoff. If it is a float type, has it been blown down frequently? Is it possible the float is sticking down?
In direct answer to your last question, @tsayles50 , The low water cutoff should shot the boiler off if the water level drops to low. Float type units can usually be checked by blowing them down with the boiler operating -- the boiler usually will shut off and the feed pilot light on the feeder should come on. Probe types are harder to check; there is a test button on them, but it doesn't really check the operation. You would need to drain the boiler down below the level of the probe and see if the boiler fires. It shouldn't. Don't forget to refill the boiler...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thank you for the guidance. Honestly, I am still trying to figure out what kind of low water cut off system I have, we moved in this past January. Any guidance on how to figure that out?0
-
Post some pics of your boiler.
Where are you located?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Have you gone through the settings on the feeder?
Questions for the steam pros.
1- Why is the stamp for minimum water level below the LWCO probe and the gauge glass? Anything to do with a false water line?
2- Does the back flow preventer serve any purpose here?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements