Nitrogen
johnjohn89
Member Posts: 114
Service experts. I have always wondered if the Nitrogen flows through the compressor when brazing it in. If nitrogen does flows through the compressor and how ? Does compressor internal discharge open let nitrogen flow through since only 1.5-2 psi ?
0
Comments
-
When brazing you only flow at extremely low pressure. (1 1/2#'s it way to high.) All your trying to do is displace any oxygen to prevent copper oxides from forming. ASSUMING something is open on the high side and there's NO control valves yes it just flows through the compressor from low to high sides.0
-
-
You need a flow gauge......
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
pecmsg said:Is this a school test question?
I ask because you posted the same thing on H-talk.0 -
pecmsg said:When brazing you only flow at extremely low pressure. (1 1/2#'s it way to high.) All you’re trying to do is displace any oxygen to prevent copper oxides from forming. ASSUMING something is open on the high side and there's NO control valves yes it just flows through the compressor from low to high sides.
and I try to find information about can nitrogen
flow through compressor but I can’t find any, do u know where I can find info about that? Thanks0 -
-
pecmsg said:Discharge valves are like a check valve, As long as flowing from low side to high side.
Although it should be unloaded if not running...Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
There is no back pressure on the discharge valves since the compressor is not running they will open under little pressure.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements