Am I the last Hydrotherm Hydropulse AM-100 owner in the world?

Options
StahlMaster
StahlMaster Member Posts: 18

Am I?

Mad Dog_2

Comments

  • SuperTech
    SuperTech Member Posts: 2,166
    Options

    No, I saw pictures of one that was still in operation last year.

  • hot_rod
    hot_rod Member Posts: 22,158
    Options

    One of a few I suspect.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options

    Are those sort of like an HTP Phoenix?

  • jumper
    jumper Member Posts: 2,260
    Options

    I remember when they were introduced.At then prevelant high interest rates there was a question if they made made economic sense. Some years later Fulton introduced much bigger pulse water heaters. I also seem to remember that Lennox offered a pulse furnace that turned out unsatisfactory.

    Mad Dog_2
  • kcopp
    kcopp Member Posts: 4,432
    Options

    I saw one in November. Its there in the home. its not running but the homeoner wants to get it operating again…

  • Mad Dog_2
    Mad Dog_2 Member Posts: 6,963
    Options

    Still see them chugging along . U got a picture of yours? What year installed? Mad Dog

  • StahlMaster
    StahlMaster Member Posts: 18
    Options
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options

    Is that a door mat under it?

  • StahlMaster
    StahlMaster Member Posts: 18
    Options

    No. That is 2 door mats under it. I think it helps with vibration and noise transmission. It under our stairwell.

    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 6,963
    Options

    Oh no! That's not an approved base for the heater! Remove at once!!!! KIDDING......looks to be in VG shape. I love that Blue AGA star...harkens back 1970s & 1980s..I'm gonna say a 1980 manufacturing date? Mad Dog

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,528
    Options

    Thete's B1994 on the label. Probably February 1994.

    Retired and loving it.
    Larry Weingarten
  • Mad Dog_2
    Mad Dog_2 Member Posts: 6,963
    Options

    Sharp Eyes Grampa Holohan better than mines! I refuse to get bi-focals... Mad Dog

  • StahlMaster
    StahlMaster Member Posts: 18
    Options

    I'm doing the 5 year service for this am-100 boiler. Can someone remind me the correct temperature setting for the high- limit. I like to check instead of relaying on the auqastat setting. It's "set" at 160 now. I have radiant baseboard radiators.

  • JohnNY
    JohnNY Member Posts: 3,231
    Options

    I see you have the flue muffler. My father installed one in our house in the…I don't know…late '80s I'd say. It was the loudest thing in the house. We put a Weil-McLain in the following year and had that boiler until Hurricane Sandy wiped it out.

    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • StahlMaster
    StahlMaster Member Posts: 18
    Options

    I hear a lot of complaints about the noise of these units. I can honestly say that has never been an issue for us in our 1,400 sq ft house. The unit is installed under our basement stairs and vent out next to the side door.

  • hot_rod
    hot_rod Member Posts: 22,158
    Options

    On a rubber pad, with the front cover on, they were not too bad. Probably noiser outside by the vent termination.

    A testament to how long a condensing heater can last. I think that was long before the controls had data logging capacity. It would bve interesting to know how may cycles it has run, I'd bet over 100,000!

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • StahlMaster
    StahlMaster Member Posts: 18
    Options

    You are right, the noise at the outside vent is both louder than other units and much more unique!

  • Alan (California Radiant) Forbes
    Options

    I serviced three of them, late 90's. Replaced one with a Munchkin and lost track if the others, thank goodness as I didn't like them. Same with GlowCore.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • StahlMaster
    StahlMaster Member Posts: 18
    Options

    Ok. This is what I observed today. I had the heat turned down to 64degrees to do this test. I have one zone valve for the house heat and one for the hot water.
    The boiler temp is 100degrees pressure is 16psi (by the gauge)
    Aquastat is set to 180degrees with a differential of 20degrees
    The temperature in the house (1400sqft) is 64degrees. I set the temperature to 68degrees.
    11:23 64 set to 68. Call for heat went on. Zone valve for heat turned boiler started.
    11:27 Boiler temp 120degrees pressure 19psi Circ ON
    11:30 Boiler temp 130degrees pressure 19psi Circ ON
    11:34 Boiler temp 145degrees pressure 20psi Circ ON
    11:37 Boiler temp 160degrees pressure 21psi Circ ON
    11:40 Boiler temp 170degrees pressure 22psi Circ ON
    11:43 Boiler temp 180degrees pressure 23psi Circ ON
    11:46 Boiler temp 188degrees pressure 24psi Circ ON
    11:50 Boiler temp 191degrees pressure 25psi House temp 65.8degrees Boiler OFF circulator ON
    11:55 Boiler temp 170degrees pressure 22psi House temp 66.3degrees Boiler ON circulator ON
    12:06 Boiler temp 191degrees pressure 25psi House temp 67.4degrees Boiler OFF circulator ON
    12:12 Boiler temp 170degrees pressure 22psi House temp 68 degrees Boiler ON circulator ON
    12:22 Boiler temp 191degrees pressure 25psi House temp 69 degrees Boiler OFF circulator OFF call for heat OFF.
    When the service guy came, he changed a bad pressure tank (28 years old, weak bladder) and changed the aquastat setting from 210degrees (it had a metal stop at that setting, NOT movable) to 180degrees.
    It appears to me that this system is working fine.
    What do the professionals think?

  • mattmia2
    mattmia2 Member Posts: 9,670
    Options

    Did you check the precharge in the expansion tank? Depending on the size of the system and size of the tank it might be fine although my guess was the precharge needed to be topped off. Settign the aquastat to 210 makes no sense, 180 or maybe a little less is where that should be depending on system design.

  • StahlMaster
    StahlMaster Member Posts: 18
    Options

    The tank has/had a precharge of 12psi.

    Thanks.

    PC7060
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options

    What are you runnign the system at? It should match the cold fill pressure of the system.

  • StahlMaster
    StahlMaster Member Posts: 18
    Options

    The cold fill pressure is 14psi.

  • mattmia2
    mattmia2 Member Posts: 9,670
    Options

    The precharge should be 14 psig then.

  • StahlMaster
    StahlMaster Member Posts: 18
    Options
    S"ettign the aquastat to 210 makes no sense, 180 or maybe a little less is where that should be depending on system design"
    What would "depending on the system design" mean exactly? I have one heating zone and one hot water. How do I determine system design.