I have a customer looking to replace their low pressure steam boilers. My competition is saying a chimney liner is required by code because it's an old brick chimney. The chimney looks to be in good condition. Do you know of a code that says a linear must be used? I have looked through every code manual I have and have found nothing that requires it.
Thanks in advance.
Thanks in advance.
Ray Wohlfarth
Boiler Lessons
Boiler Lessons
0
Comments
-
Hello Ray;
I believe the International Mechanical Code (IMC) requires all masonry chimneys to be lined. As an example, please take a look at Section 801.16 of the current Michigan Mechanical Code. The Michigan Code, as are many local codes across the country, is modeled after the IMC.
Link to exact code language is here: https://up.codes/viewer/michigan/mi-mechanical-code-2015/chapter/8/chimneys-and-vents#8 Scroll down to section 801.16
In any event, even if it wasn't code required, in my opinion, a masonry liner is a REALLY good idea and best practice. I'd never recommend a modern gas/fuel oil boiler be operated with an unlined chimney.
Hope this helps!
Mike Gordon0 -
When you say brick chimney does it have a clay liner? Or is it a really old unlined chimney? Inside chimney or outside? Oil or gas?
0 -
-
-
Can you measure velocity and temperature at top of chimney?
If there is no chance for liquid to condense on surface.....0 -
In NYS, Chimneys with a direct exposure to the outside elements and temperature require a "liner." Some inspectors say an intact terracotta clay liner suffices. Others will tell you, they want a sleeved "slinky" inserted down the existing chimney and to the breech. Interior chimneys (very old hones usually) if terracotta-clay lined will suffice. In general, I'm usually going to recommend and insulated stainless steel "slinky." It can only help. Mad Dog0
-
@jumper I would need a really big ladder and I would never be able to go that high LOL Thanks
@Mad Dog_2 I think they are looking at a liner or sidewall venting. ThanksRay Wohlfarth
Boiler Lessons0 -
May be easier to abandon chimney. Blow exhaust through recuperator and new flue.RayWohlfarth said:@jumper I would need a really big ladder and I would never be able to go that high LOL Thanks
@Mad Dog_2 I think they are looking at a liner or sidewall venting. Thanks0 -
Or rent a towable lift that can reach that high ($$$).0
-
@jumper Thats what I was thinking. Just sidewall vent the boilers through the wall next to the chimney
@SteamingatMohawk Can't imagine the price for thatRay Wohlfarth
Boiler Lessons0 -
Sidewall venting might be easier said than done. That looks like a walkway next to the building, which IIRC would require a sidewall vent to be 7 feet above grade. At that level you're well into the first floor.RayWohlfarth said:@jumper Thats what I was thinking. Just sidewall vent the boilers through the wall next to the chimney
@SteamingatMohawk Can't imagine the price for that
Then there are the additional moving parts required for sidewall venting, which always break down in the middle of winter.
A stainless-steel chimney liner has its merits.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Venting the Rinnais, or any tankless or wall hung boiler is the worst part of the job. Mad Dog0
-
@Steamhead Good points thanks
@Mad Dog_2 The good part of this is I won't be installing it. I will just sell the boilersRay Wohlfarth
Boiler Lessons0 -
-
Good joke. Get a guy with a drone to measure temperature & air velocity at top of chimney. If there is enough draft CO2 blows right out without condensing or condensate blows out without eating bricks? I really don't know but I do know that there were unlined chimneys that last decades. Maybe soot protected the masonry then?SteamingatMohawk said:Hey, maybe you can get a good deal on one of those Chinese spy balloons for an afternoon. Bad joke...LOL
Another thing to worry about is ice when boiler is too efficient. How much help is lining for that?0 -
-
A building like that may cry out for an engineered flue design. Or a design produced by the manufacturer of the vent material being considered. Selkirk for example.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
@RayWohlfarth
Maybe look at a new chimney? Something like a Selkirk type exposed chimney. Abandon the old one.
Might be more cost affective?0 -
@hot_rod Im leaving it up to the owner now. He hired an engineer and I believe they are going with a new flue liner
@Intplm. The owner hired an engineer. Last I heard, they were installing a liner
Ray Wohlfarth
Boiler Lessons1 -
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements