Shouldn’t this be 2.5 psi?
Shepfitz_03
Member Posts: 4
I have a a fairly new gas boiler (8 yrs old)for my steam heat. What would cause it to be that high and is it dangerous? Thanks!
0
Comments
-
Hello @Shepfitz_03,
Oversized boiler.
Presuretrol or Vaporstat not working correctly.
Plugged up pigtail pipe to the Presuretrol or Vaporstat.
Gauge is broken and reading incorrectly.
It probably should be way below 2.5 Lbs. like that gauge never moves.
I would find out what is going on.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
-
Sounds like this is a new thing, it didn't run at 10 psig before?
Short answer, yeah. It almost certainly should be lower than 10. The cause can be anything from fairly benign (defective gauge) to a rather serious fault (failed safely controls). Has any work been performed recently? The most common cause is simple incompetence (adjusting the set point higher than it should be).
2 -
should be less than 2, lower the better,
known to beat dead horses0 -
Picture of the glass tube. Did have someone look at it a year ago and he cleaned out the pigtail but no change. Could it be it is not vented in the basement? 2nd picture is where it may have been vented at one time in basement??0
-
Hello @Shepfitz_03,
When the boiler is off does the gauge eventually return to zero ?
When the boiler fires up can you watch the gauge go from 0 to 10 PSI ?
A missing Main vent should not raise the pressure significantly, since it should be the first vent to close anyway. If it is missing the Steam distribution in the main pipe is not as efficient as it could be.National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
-
so this thing has been running up to 10 psi for over a year?
and no one has been able to figure why?
if you pull one wire off the Ptrol, and thermostat calling,
will the boiler still fire?
it should not.
as asked above,
does the gage return to ZERO ?known to beat dead horses0 -
That asbestos is deteriorating and will get worse. Hit it with your head and it will discharge. Banks are getting stricter with reserves for removal on mortgage approvals.John Cockerill Exquisite Heat www.exqheat.com Precisions boiler control from indoor reset.0
-
Might want to pull the cover off the pressuretrol and check the white differential wheel. Set to 2 lbs and see what happens.
John Cockerill Exquisite Heat www.exqheat.com Precisions boiler control from indoor reset.0 -
Shut the boiler off. The gauge should go to 0 if it doesn't it's a bad gauge0
-
It does go to 0 when off. Having someone look at it tomorrow- will pass all your suggestions and let you know Tks0
-
Safety issues aside, your radiator vents are probably toast also since they only like to run up to a couple of psi. Try and get some main vents on there and double check that your radiators are heating evenly across and all roughly at the same time.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements