And that's an older panel with the cube relays. Any reason why it's a question years after it was installed, or just curious? Because now I'm curious.0
-
It also closes the circuit to the associated pump, turning it on.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
The answer is yes. That thermostat wire that is connected to it goes to the TT connection in the boiler aquastat turning on the boiler.0
-
I have asked this question because I suspect that the relay which controls the XX terminals may be faulty. At random times, my burner may not fire even though the circulators are running. It happens infrequently. I can always start the system again by simply turning off the AC power, waiting a minute, then turning the power back on. I wonder if one of those relays is sticking at random times.0
-
Yes, I've had that happen as well. Some of the newer controls give you additional end switches, but this one doesn't.
I usually replace the control, but maybe there's a repair. Someone from Taco is bound to make an appearance here and let us know. @SteveSan or @Joe Mattiello8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
-
Is the one with the metal clip a spare relay?0
-
Is the one with the metal clip a spare relay?
The first one with the metal clip is a 120v for zc/zr. Second one is for the end switch ( 24v ) and 3-8 are for the zones starting with zone 1.
You can switch out one of the relays from 3-8 for the end switch ( 2nd ) to see if the relay is starting to go.
If you are still having issues with the end switch it might be just the age of the board and would need to be replaced with a newer SR506-4.
If you have any questions, please give Taco Technical Services a call during normal business hours Mon-Fri 8am-5pm EST 401-942-80003 -
Good question! I don't know the answer. I do know the leftmost relay is 120/110 VAC. The others are 24 VAC0
-
If the relay which controls the XX terminals is stuck open, will there be a voltage reading across the XX terminals?
0 -
XX on the Taco board is a dry contact, but if the boiler is on, you might get a reading off the transformer in the boiler even though it's only one leg............I think. Never tried.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
I have asked this question because I suspect that the relay which controls the XX terminals may be faulty. At random times, my burner may not fire even though the circulators are running.
I have some questions about that statement. Is it the wiring between the SR and the boiler aquastat, the relay in the aquastat, something in the boiler wiring, Is the boiler at high limit, etc. You could jump the XX terminal when the problem happens and see if the boiler fires. You could jump the TT connections in the boiler aquastat and see if it fires. You could check the continuity on the XX terminals with a continuity meter when this happens. Disconnect the current wires to the boiler when you do a continuity test. Touch the present at the XX termials wires to the boiler together and see if the boiler fires. You need to diagnosis this further.
Personally, I don't think it's the relay in the SR.1 -
Is one of these the boiler aquastat??? It's a Buderus GB142
0 -
nonobar said:Is one of these the boiler aquastat??? It's a Buderus GB142
However XX from the Taco panel should connect to position 3 (WA-Green) on the connection board.
If a circulator is running and XX is closed (working) then there should be 0 volts a XX. If XX is open (not working), it will read either 10vac or 24vac. Not sure which because Buderus uses a multi volt transformer.0 -
I think I know what you are asking, BUT you are using the incorrect terminology.nonobar said:When a thermostat calls for heat, does the relay in the TACO unit simply provide a short circuit at the XX terminals?
A short circuit (sometimes abbreviated to short or s/c) is an electrical circuit that allows a current to travel along an unintended path with no or very low electrical impedance. This results in an excessive current flowing through the circuit.
Your question should be "When a thermostat calls for heat, does the relay in the TACO unit simply provide a completed circuit or a set of dry open contacts to close?"
@109A_5 is the self proclaimed expert on short circuits. I'm surprised he has not weighed in on this post.
Film at 11Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
If your boiler is above low limit, it won't fire when a TT is calling for heat until it falls below that temp.nonobar said:I have asked this question because I suspect that the relay which controls the XX terminals may be faulty. At random times, my burner may not fire even though the circulators are running. It happens infrequently. I can always start the system again by simply turning off the AC power, waiting a minute, then turning the power back on. I wonder if one of those relays is sticking at random times.
0 -
What would make the boiler go above "low limit"?Duckbutter said:
If your boiler is above low limit, it won't fire when a TT is calling for heat until it falls below that temp.
0 -
I believe that @Duckbutter means High limit. The boiler you have does not have a low limit. It does modulate based on outdoor the return water temperature, and perhaps the outdoor temperature if you have one connected.
But to answer your query about why it might be above a temperature where the burner will not run... If zone DHW just finished a call for heat and zone 2 just started a call for heat, the boiler may do a self check to determine the water temperature at the supply and the return, and finds there is a high enough temperature in the system to wait for the burner to fire until the water temperature drops to a point where more heat is needed. It also depends on wether the DHW Circulator is wired to the boiler control or the zone control.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Ed, I did mean "low", just hadn't read past the initial description, hadn't realized this is a modulating Buderus and assumed it was a standard boiler.
You perfectly illustrate my point though, if the water is already hot, it won't run while the circ's on.
0 -
The boiler fails to fire infrequently, and when it does, the cast iron baseboards are stone cold.Duckbutter said:Ed, I did mean "low", just hadn't read past the initial description, hadn't realized this is a modulating Buderus and assumed it was a standard boiler.
You perfectly illustrate my point though, if the water is already hot, it won't run while the circ's on.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements