Slight Gas Smell when Steam Boiler Firing Up
I have a Weil McLain boiler that was installed back in 2015. I was in my boiler room and noticed a slight gas smell with it first fired up. It’s similar to when you turn on your stove.
is this normal or do I need to get this checked? The smell is gone quickly after.
Comments
-
Most likely normal from your description.NJHomeowner said:Hello,
I have a Weil McLain boiler that was installed back in 2015. I was in my boiler room and noticed a slight gas smell with it first fired up. It’s similar to when you turn on your stove.
is this normal or do I need to get this checked? The smell is gone quickly after.
When it first fires there's very little if any draft.
I assume this is an atmospheric vent boiler? Can you share some pictures so we can confirm?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Thanks. I do, it vents through my chimney.0
-
What a nice installation. Ezzy, Johnny, or Dave I wonder?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el2 -
-
We certainly miss him in North Jersey!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Is he ok? Also any concerns on the gas smell?0
-
He's fine last I heard, he's just working for PSE&G now and I'm sure his blood pressure is greatly lowered not being a small business owner anymore LOL
I wouldn't be concerned if it's just momentary like that. Strangely mine never makes that smell--I would actually expect it to once in a while.
I'd have a decent CO detector above the boiler just because it's super cheap and nice insurance.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
Spending a lot more time near mine lately I have caught a wiff a few times.ethicalpaul said:He's fine last I heard, he's just working for PSE&G now and I'm sure his blood pressure is greatly lowered not being a small business owner anymore LOL
I wouldn't be concerned if it's just momentary like that. Strangely mine never makes that smell--I would actually expect it to once in a while.
I'd have a decent CO detector above the boiler just because it's super cheap and nice insurance.
It's literally just a hint of mercaptan which is so easy to smell.
I almost typed marzipan.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
Nice!
Thanks, I have one in the room about 10 feet from it0 -
@NJHomeowner
If it is lighting smooth it is probably ok. If it lights with a rough snap like roll out than have it checked2 -
I smell a whiff of gas too if I'm standing in the boiler room when it comes on. I tried fussing with the pilot to see if I could make the burners light quicker, but nothing seemed to help.
That is surprising since you don't have a standing pilot. Wouldn't you think a standing pilot would light the burners quicker than that sparky thing?ethicalpaul said:Strangely mine never makes that smell--I would actually expect it to once in a while.
Last time I had a flue gas analysis, CO was 0 ppm. I could almost do without the flue, let alone the CO detector.ethicalpaul said:I'd have a decent CO detector above the boiler just because it's super cheap and nice insurance.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-241 -
That is surprising since you don't have a standing pilot. Wouldn't you think a standing pilot would light the burners quicker than that sparky thing?
Well the sparky thing only lights the pilot, which then lights the burners so probably not a big difference there.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
But still, the gas starts coming out of the pilot before it gets lit. It may be a smaller amount, but it would be in addition to the gas from the burners before they light.ethicalpaul said:Well the sparky thing only lights the pilot, which then lights the burners so probably not a big difference there.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
It starts sparking before it turns gas on to the pilot, then once that's lit it turns on the main burners which light just as they do with a standing pilot.Hap_Hazzard said:
But still, the gas starts coming out of the pilot before it gets lit. It may be a smaller amount, but it would be in addition to the gas from the burners before they light.ethicalpaul said:Well the sparky thing only lights the pilot, which then lights the burners so probably not a big difference there.
They do everything they can to avoid the possibility of a delayed ignition.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I have an EG65 installed same time period (2014). Noticed same thing since day 1 but it has not changed or gotten worse. Only smell it in the near vicinity of the boiler. Thought maybe the auto flue damper just was keeping the chimney a bit cooler so less initial draft. Nothing close to a rollout so didn't worry about it.0
-
I'm sure they do, but it's not perfect. I mean, I light my pilot once in the fall and it stays lit all winter, so, all things considered, an electronic ignition must cause more gas to escape, even if only a slight amount. I don't see how it could allow less.ChrisJ said:It starts sparking before it turns gas on to the pilot, then once that's lit it turns on the main burners which light just as they do with a standing pilot.
They do everything they can to avoid the possibility of a delayed ignition.
Come to think of it, I'm not sure how comfortable I am with the idea of electronic ignitions. If there's even the smallest leak in your gas plumbing, you could build up a sizeable cloud before you get a spark or open flame to set it off, and a gas explosion can ruin your whole day. I can see where they might be a little more efficient, but safer? I don't think so.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
No idea.Hap_Hazzard said:
I'm sure they do, but it's not perfect. I mean, I light my pilot once in the fall and it stays lit all winter, so, all things considered, an electronic ignition must cause more gas to escape, even if only a slight amount. I don't see how it could allow less.ChrisJ said:It starts sparking before it turns gas on to the pilot, then once that's lit it turns on the main burners which light just as they do with a standing pilot.
They do everything they can to avoid the possibility of a delayed ignition.
Come to think of it, I'm not sure how comfortable I am with the idea of electronic ignitions. If there's even the smallest leak in your gas plumbing, you could build up a sizeable cloud before you get a spark or open flame to set it off, and a gas explosion can ruin your whole day. I can see where they might be a little more efficient, but safer? I don't think so.
I preferred a pilot light on a kitchen stove as it seemed much more reliable.
But, with the huge push for "efficiency" on everything regardless of how practical it is, this is where we're at.
A pilot light generally had a thermocouple that could fail over a long time, maybe the orifice would get a little dirty.
Electronic ignition has all kinds of fun stuff that can cause problems and it costs a small fortune to buy and replace. Everyone always talks about how much a pilot light costs to run but no one discusses what it costs to use electronic ignition. The total cost, start to finish including replacement modules, troubleshooting labor costs etc.
My dad used to let the pilot light on his furnace run 24/7 365 days a year. I think he probably lit it a total of 2 or 3 times in the 28 years he owned that house. He felt turning it off in the summer was asking for issues, so he just let it run. Apparently the cost of gas usage wasn't enough for him to care.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I've replaced the thermocouple twice. I'm surprised they last as long as they do being red-hot all the time.
I light the pilot every year, but it takes a few minutes to purge the air from the line. This tells me there must be a slow leak somewhere, but even with a gas detector, I've never been able to find it.
When I light it, I hold the lighter under the thermocouple to pre-heat it while I'm waiting for the gas to get there so I don't have to wait another minute for the pilot to heat it up after the gas comes on.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
IMO, the electronic ignition is safer in that if you have flame failure with the main gas valve energized, the system responds within about 2 seconds to drop out power.
The old school T-couples can take well over 30 seconds to shut down all gas.
That is a long time to listen to the main gas flowing waiting for shut down when testing the T-couple safety.
I had a NG 960,000 BTUH boiler from 1963, with 4 pilots/T-couples, which took almost 90 seconds to shut down the main gas valve. The longest counting I ever had.....and to think that originally it was Propane....and is still in a nursing home.1 -
Under what conditions would the main burner and all 4 pilots blow out?JUGHNE said:IMO, the electronic ignition is safer in that if you have flame failure with the main gas valve energized, the system responds within about 2 seconds to drop out power.
The old school T-couples can take well over 30 seconds to shut down all gas.
That is a long time to listen to the main gas flowing waiting for shut down when testing the T-couple safety.
I had a NG 960,000 BTUH boiler from 1963, with 4 pilots/T-couples, which took almost 90 seconds to shut down the main gas valve. The longest counting I ever had.....and to think that originally it was Propane....and is still in a nursing home.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Dirty burners, delayed ignition of the main burners, plugged heat exchanger, down draft on venting, any number of situations.
I may be over concerned about these things as the last person to touch it ends up owning it for some time.
The 4 pilots are in series, if any one of them fail then the T-couple circuit system opens after the time delay.
This is a pretty scary boiler room, 2 commercial water heaters and mop sink are crammed into this room along with the boiler. A 60 gallon compression is in the attic above the boiler.
There is a large kitchen exhaust hood just down the hall from this. The door is "usually" closed.
There is a huge combustion air inlet that can lead to frozen pipes, I and also the Fire Marshall have found this opening closed in the winter and we both have stated warnings of the dangers.
Of course, as the FM has power to shut the facility down, his warnings are heeded much more than mine.
But a variety of maintenance people cobble jack these things up. FM might show up once a year not necessarily in the winter time.
We completely cleaned the boiler in 2016, was last called to check controls/safeties in 2019.
So it has all the making of the "perfect storm".
I haven't been there for years so may not "own" it anymore.
0 -
It's been going for 60 years so far.JUGHNE said:Dirty burners, delayed ignition of the main burners, plugged heat exchanger, down draft on venting, any number of situations.
I may be over concerned about these things as the last person to touch it ends up owning it for some time.
The 4 pilots are in series, if any one of them fail then the T-couple circuit system opens after the time delay.
This is a pretty scary boiler room, 2 commercial water heaters and mop sink are crammed into this room along with the boiler. A 60 gallon compression is in the attic above the boiler.
There is a large kitchen exhaust hood just down the hall from this. The door is "usually" closed.
There is a huge combustion air inlet that can lead to frozen pipes, I and also the Fire Marshall have found this opening closed in the winter and we both have stated warnings of the dangers.
Of course, as the FM has power to shut the facility down, his warnings are heeded much more than mine.
But a variety of maintenance people cobble jack these things up. FM might show up once a year not necessarily in the winter time.
We completely cleaned the boiler in 2016, was last called to check controls/safeties in 2019.
So it has all the making of the "perfect storm".
I haven't been there for years so may not "own" it anymore.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements