Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Question about Hoffman Model 1A Vents
pcolburn2
Member Posts: 25
Apologies if this is a rudimentary question.
If the top nut on the Hoffman 1A is not screwed down firmly on the bottom nut, will this allow steam to escape and water loss to occur at the boiler?
I am chasing down some water loss in a multi-family building and noticing lots of loose nuts on the vents.
If the top nut on the Hoffman 1A is not screwed down firmly on the bottom nut, will this allow steam to escape and water loss to occur at the boiler?
I am chasing down some water loss in a multi-family building and noticing lots of loose nuts on the vents.
0
Comments
-
It shouldn't let steam or water escape if it's loose -- but it will lose its adjustment almost immediately, and those are finicky enough to begin with.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 891 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements