Utica boiler 95m-200 E02 error
sprynda
sprynda Member Posts: 5
I have a utica boiler model 95M-200. The boiler is triggering an E02 error message. The unit is about 15 years old. about 2 years ago the main heat exchanger was replaced. I have had the install company hear 3 time and my Propane provider twice. the unit has been maintained and cleaned. the boiler keeps turning off with error code e02. the flame sensor was replaced and the gas regulator was replaced. according to the technician all voltages appear to be normal. also did what utica tech support suggested. any suggestions ? thanks
sam
  • Ironman
    Ironman Member Posts: 7,918
    What does the manual say that E02 means?
    Bob Boan
  • sprynda
    failure to ignite.
  • Ironman
    Has the igniter been replaced?
    Bob Boan
  • sprynda
    not sure, waiting to hear from install company
  • Ironman
    The original burner on that boiler required an upgrade that included a new control module and pressure switches. Was that ever done?
    Look at the white tag on the module and see if it says “Wor gas”.
    Bob Boan
  • sprynda
    where is that tag located
  • Ironman
    On the control module.
    Bob Boan
    109A_5 Member Posts: 4,162
    Hello @sprynda,
    All this has been verified ?
    From the manual.
    https://uticaboilers.com/wp-content/uploads/2022/02/3024.pdf
  • sprynda
    i believe that the service tech checked all that. i know the voltage reading x1-5 to ground was 3 volts. the gas pressure was 11.0 a ground wire was added from heat exchanger to ground. i will pass on to tech.