Radiator angle

leaking
Member Posts: 128
One pipe system, what to be to much of an angle back to the supply, how would it affect the heat output. I have radiators raised 1-3 degrees some maybe more .
0
Comments
-
So long as there is adequate pitch back to the inlet, you're fine. What is adequate? 1/8 inch per foot probably isn't really enough. Quarter inch works. There is no maximum.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0