Boiler Replacement- Circulator placement on radiant floor zone

heidleml
Member Posts: 36
My technician installed a zone circ on the hot supply to the mixing valve instead of on the mixed side. Customer is not getting adequate heat and my tech says it will be pretty difficult to get the circ on the mixed piping. He said he can move the circ to the return side as it comes back to the boiler. I understand pumping away etc. and that this isn't ideal, but any reason it won't work?
Other zones are pumping away to high temp and working fine.
Other zones are pumping away to high temp and working fine.
0
Comments
-
-
so return will do the trick0
-
Maybe. If it's before the connection back to the mixing valve. It's not ideal, however, as the pressure at its inlet will be low -- and maybe too low for long life for the pump. Surely there is enough pipe work somewhere between the outlet from the mixing valve and the beginning of the loops? A pump isn't all that long. Someone is not thinking.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
One should pump away from the mixing valve (the mixed port), but not everyone does what they should do.0
-
Any 3 way mixing valve, manual or thermostatic, has 2 inlet ports and 1 outlet or mixed port.
To work properly and adequately you need to flow out, or pump out of the mixed port. That allows flow to enter the H&C port, blend to the appropriate temperature.
I doubt you will get a consistent or accurate temperature pumping into either inlet port.
Depending on the design of the thermostatic cartridge inside the valve could lock up or close off one of the inlet ports if you are pumping into it. If it is a ASSE 1070 valve, it is considered a scald guard type and will fail to mix. There is both a pressure and temperature component and acceptable range on 3 way thermostatic valves. An ASSE 1017 may flow, but will not mix properly.
I’d come up with a way to do it correctly. It’s the reason the ports are labeled🤔
Now different brands of mix valves have different port locations. You should have H, C, and mix.
Some valves may have A, B, and ABBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements