Grundfos Alpha2 for Radiant Heat
VancouverG
Member Posts: 33
I’m thinking about switching my Taco 007 to Grundfos Alfa2 15-55. I have 6 zones and of course the Taco pumps the same if 1 or 6 zones are calling for heat. I have two questions
1) my Taco 007 gets power thru the Taco ZV406 (picture attached). My original plan was to get the terminal box Alpha2 instead of the line cord. However My understanding is that the Alpha2 auto adapt feature would reset if the power is cut off after the call for heat is satisfied. So pointless as it would have to relearn each day. Is there a work around for this ?
2) what is a good GPM to have and have others that are using it happy or would you say stick with the Taco 007
1) my Taco 007 gets power thru the Taco ZV406 (picture attached). My original plan was to get the terminal box Alpha2 instead of the line cord. However My understanding is that the Alpha2 auto adapt feature would reset if the power is cut off after the call for heat is satisfied. So pointless as it would have to relearn each day. Is there a work around for this ?
2) what is a good GPM to have and have others that are using it happy or would you say stick with the Taco 007
0
Comments
-
The ECM delta p circs can just stay powered up. They only draw about 7 watts when in idle mode, hence the power cord and plug.
You could wire it into the relay, either switched or constant power from the box.
The two circs are similar in capacity. An ECM will both adjust its flow and also save you some powerBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
So I don’t need the terminal box model then I could go with the line cord model ? The reason I ask is that the line cord model is more available to me. If I’m understanding you correctly if I plug it in with a line cord there will not be any circulation as the zone valves are shut and so there is no where to circulate to.Also one more question I have heard others complain that they are only get .4 or .5 GPM on auto adapt. Is that a possibility? I mean what is a good GPM that I should expect0
-
I have the corded model grundfos in my own house and am very happy with it0
-
-
Dave H_2 said:The 007e will do what you are looking for. The most efficient circulator is the one that is powered down. It will speed up and slow down as the actuators open and close0
-
VancouverG said:So I don’t need the terminal box model then I could go with the line cord model ? The reason I ask is that the line cord model is more available to me. If I’m understanding you correctly if I plug it in with a line cord there will not be any circulation as the zone valves are shut and so there is no where to circulate to.Also one more question I have heard others complain that they are only get .4 or .5 GPM on auto adapt. Is that a possibility? I mean what is a good GPM that I should expect0
-
I too don't understand the ecm thing. So basically the alpha should be powered on all the time and it's ok to deadhead it with a zone valve closed? Does the ecm stop the rotor from turning at all until the zone valve is opened? I too have an alpha on a radiant manifold and I don't use the auto-adapt as it's switched on with the zone relay.0
-
I use my Alpha2 in delta-P mode and relay switch it on/off via end-switches in the zone actuators.
30+ yrs in telecom outside plant.
Currently in building maintenance.0 -
Jlinde37 said:I too don't understand the ecm thing. So basically the alpha should be powered on all the time and it's ok to deadhead it with a zone valve closed? Does the ecm stop the rotor from turning at all until the zone valve is opened? I too have an alpha on a radiant manifold and I don't use the auto-adapt as it's switched on with the zone relay.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Auto adapt is over rated hype. Just switch in and put it in one of the constant pressure modes,"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
-
The 007e ECM will run most efficiently because it runs close to synchronous speed, or less slip like traditional PSC 007. As Dave said, you can get more efficient pump than one that powered down when there’s no load.hope this helpsJoe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions2
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements