Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

steam boiler size

Options
replacing a weil mclain 256 input BTU steam boiler 12 cast iron radiators in the building can I use a 187BTU steam boiler?

Comments

  • morganheating
    morganheating Member Posts: 2
    Options
    building well insulated and new everything, old unit from1956 customer wants to know. I can replace will a 200BTU unit but calculation charts seem vague
  • ethicalpaul
    ethicalpaul Member Posts: 5,704
    Options
    You have to measure the EDR of the existing radiation in the building then compare that to the "Net Sq. Ft. of steam" value on the boiler spec/plate.

    The existing boiler size is meaningless. The BTUs can be ignored. The number of radiators is by itself meaningless.

    Match EDR to sq. ft. of steam and be one of the 1% of HVAC contractors who does it right.
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
    bburd