Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
steam boiler size
morganheating
Member Posts: 2
replacing a weil mclain 256 input BTU steam boiler 12 cast iron radiators in the building can I use a 187BTU steam boiler?
0
Comments
-
building well insulated and new everything, old unit from1956 customer wants to know. I can replace will a 200BTU unit but calculation charts seem vague0
-
You have to measure the EDR of the existing radiation in the building then compare that to the "Net Sq. Ft. of steam" value on the boiler spec/plate.
The existing boiler size is meaningless. The BTUs can be ignored. The number of radiators is by itself meaningless.
Match EDR to sq. ft. of steam and be one of the 1% of HVAC contractors who does it right.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements