Whining/Droning Noise from Triangle Tube Boiler
Kynes1000
Member Posts: 5
We have a persistent whining/droning noise coming from our 18-month old triangle tube boiler (we moved into the house 6 months ago so inherited it). The whining noise occurs when the radiant floors or radiators call for heat.
The boiler powers 3x radiant floor zones (tekmar thermostats) and 2x radiators. It also heats the indirect domestic hot water storage tanks.
The hot water tanks don’t seem to cause the noise. However, if any of the radiant or radiator zones call for heat the noise starts. It’s driving me crazy. Noise can be clearly heard inside and even louder from the exterior exhaust pipe. I am in Chicago and have had a few people out to look but no success.
Any thoughts or suggestions would be appreciated!
The boiler powers 3x radiant floor zones (tekmar thermostats) and 2x radiators. It also heats the indirect domestic hot water storage tanks.
The hot water tanks don’t seem to cause the noise. However, if any of the radiant or radiator zones call for heat the noise starts. It’s driving me crazy. Noise can be clearly heard inside and even louder from the exterior exhaust pipe. I am in Chicago and have had a few people out to look but no success.
Any thoughts or suggestions would be appreciated!
1
Comments
-
-
-
The boiler model is a Triangle Tube Instinct Solo Wall 110. Had the original installer out who said no fan issue he could see.
Low fire - I am not sure the answer to this question as don't know my way around a boiler/radiant well enough... How would I figure that out?
Combustion Analysis - They did NOT run a combustion analysis. Original boiler installer informed me they had run a combustion analysis at install. They could do it again. I had mentioned to him that the exterior exhaust smelled like gas more than I thought it should. He checked it out and it didn't smell strong to him but, again, mentioned they could run the combustion test.1 -
-
If a combustion analysis and proper adjustments toward the richer end of the manufacturer’s chart doesn’t fix it, then CSST used in the gas line is the likely culprit.
https://forum.heatinghelp.com/discussion/164856/csst-the-cause-of-harmonic-fog-horn-noise#latest
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.3 -
Thank you - that makes sense. I will have them do a combustion analysis.
Interestingly enough, it was near zero degrees in Chicago yesterday and I only heard the boiler make the noise once. I’m guessing maybe it was in high fire given the cold temp. So, maybe it is only happening in low fire.0 -
just wanted to update that adjusting towards richer end fixed the harmonic noise. We ended up getting on the phone with triangle tube support as there were some more detailed/complicated adjustments that could be made (I don't understand all of it) and that did the trick. Thanks to everyone for the input and thoughtful answers!
1 -
Out of curiosity is this set up with LP or natural gas?
0 -
Natural gas0
-
Improper combustion set up, CSST gas piping and/or undersized gas piping can all cause unwanted harmonics.0
Categories
- 121.3K All Categories
- 84K THE MAIN WALL
- 2.9K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 40 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.7K Gas Heating
- 119 Geothermal
- 155 Indoor-Air Quality
- 3K Oil Heating
- 56 Pipe Deterioration
- 771 Plumbing
- 5.4K Radiant Heating
- 362 Solar
- 14K Strictly Steam
- 3K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 73 Job Opportunities
- 17 Recall Announcements