In-floor radiant heat help
I've got in-floor radiant heating in my office which is an extension of my garage.
Worked like a charm until we had a bad cold spell for about a week. Now it still kicks on, but no heat whatsoever.
I changed the thermostat hoping that was it. Didn't fix it. Also closed off the valves and released the air - no help.
It's a Rheem water heater. Both circulation pump sound/feel to be working fine. But the water heater (and pipes) are cold to the touch.
No pressure on gauge.
Here is the setup:
https://drive.google.com/file/d/1TjzjhKQdOaoBgklJtxyDTmc7bqoxkhf4/view?usp=sharing
https://drive.google.com/file/d/1irLINZyMFDZoJrLaNjzfHzj88_eNt_kt/view?usp=sharing
Any help is greatly appreciated!
  • Ironman
    Ironman Member Posts: 7,926
    Have you checked to make sure that you have power to the water heater? The high limit isn’t tripped?
    It could also be a bad thermostat or heat element.
    Bob Boan
    hot_rod Member Posts: 27,815
    could be a frozen area near the door?
  • bwoodard28
    bwoodard28 Member Posts: 7
    Not sure about the heat element but I did check the power and replaced the thermostat to be safe.
  • bwoodard28
    Would a frozen area by the door cause the whole system to stop working or just that zone?
    EdTheHeaterMan Member Posts: 12,497
    edited January 2023
    You need to go thru the process of elimination.
    1. You say the water heater is not hot.
    2. Do you have power to the water heater? How are you measuring for power?
    3. Does the Power go thru the thermostat to the element?
    4. Is the element in the water heater working? A shorted or open element will cause no heat
    That is where I would start.
    If a water heater is powered and there is no water in the tank, the elements will overheat and fail.
    bwoodard28