Steam low water problem

sixtog
sixtog Member Posts: 10
This is driving me crazy already i usually pipe a PSE 800 m before the Harford loop because slant fin don't have an outlet for a secondary low water cutoff on the boiler itself, but i keep getting called back because boiler is not working. the boiler has water. If i reset it comes on it is not the probe i clean it and it only happens on this type of boiler i do the same thing with Williamson boiler and it's great the equalizer is  1"1/2  i know i should have brought it down 2"1/2 but not sure if it would had made a difference

Comments

  • Long Beach Ed
    Long Beach Ed Member Posts: 1,320
    edited January 2023
    You get lots of steam bubbles in that loop. It varies with the boiler design. The steam that's made in the base of the boiler rises in that equalizer just as it rises in the boiler.

    It's a bad place for a low water cutoff. That's my thought.
  • ethicalpaul
    ethicalpaul Member Posts: 6,667
    I can't imagine steam bubbles forming or traveling there. Is it possible the boiler is throwing water (surging) its water into the mains and the level is actually dropping that far?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,477
    I agree with @ethicalpaul

    Is the boiler water surging or bouncing? Was the boiler skimmed?
  • sixtog
    sixtog Member Posts: 10
    I skimmed the boiler but the water doesn't seem like it's bouncing too much. I do have that problem in another job with the same type of boiler and I've been skimming almost every 2 weeks and the water gets stable, but when I come back to check on it, the water is bouncing like crazy. i have the same problem there with the secondary low water cut off going out. It's hard for me to see if the boiler is surging since I'm not there when it happens and I can't see inside. 
  • pedmec
    pedmec Member Posts: 1,066
    Is your near boiler piping and pipe size installed per manufacturers specifications?

    are you skimming correctly? getting the boiler water temperature just below steaming and then skimming. using a large skim port to remove as much surface water as possible, larger than a 3/4" opening.
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,320
    edited January 2023
    For now, why not swap the resettable and non-resettable cutoffs? While the boiler will cut in and out, you won't get the lock-out call. And your customer won't lose all his heat.
  • JUGHNE
    JUGHNE Member Posts: 11,276
    Or if you remove the boiler drain bib, add a nipple/tee there, put the bib back on the

    bull of the tee and the LWCO on the open run.

    That would lower it a few inches.......actually too low for safe operation.....but a temp try.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,477
    Skim with TSP using Dan Holohan's method works every time. 1 2 hour skim and your done.
  • JUGHNE
    JUGHNE Member Posts: 11,276
    How close is the probe to the back of that tee?

    (thinking of expansion/contraction of probe)

    Will these lock out if the probe becomes grounded??