Help Fitting Upgraded Main Vent in Tight Space
alexh
Member Posts: 10
Hello all,
I have crappy Home Depot venting through my house on my 1 pipe steam heat system and finally ordered all new Gorton vents for the mains and radiators. I determined I need one Gorton #1 (to vent 27' of 2.5" pipe) and one Gorton #2 (to vent 77' of 2.5" pipe).
My first question relates to the linked images below. There is 11" between the header T and the ceiling. If I were to add a 4" nipple (is this long enough?), the Gorton #2 would clear the ceiling by a quarter inch, but I wouldn't be able to turn it since the joist is in the way. What's the optimal solution here? Do I use a few elbows to get away from the joist? If so, how do I ensure there's no horizontal piping on the way to the main vent?
https://imgur.com/a/BR6WQbK
Thanks for your help,
Alex
I have crappy Home Depot venting through my house on my 1 pipe steam heat system and finally ordered all new Gorton vents for the mains and radiators. I determined I need one Gorton #1 (to vent 27' of 2.5" pipe) and one Gorton #2 (to vent 77' of 2.5" pipe).
My first question relates to the linked images below. There is 11" between the header T and the ceiling. If I were to add a 4" nipple (is this long enough?), the Gorton #2 would clear the ceiling by a quarter inch, but I wouldn't be able to turn it since the joist is in the way. What's the optimal solution here? Do I use a few elbows to get away from the joist? If so, how do I ensure there's no horizontal piping on the way to the main vent?
https://imgur.com/a/BR6WQbK
Thanks for your help,
Alex
0
Comments
-
-
Go as high as you can but leave a little space just below flooring above for future removal. You CAN pipe them over and away to achieve this but just make sure you pitch the nipples and piping BACK toward the main. I like to use Blue Monster and Megaloc for the joints, so they are easy to come out down the line. Good Luck Mad Dog0
-
I forgot to add, because I didn't know this either in the beginning, but wash all of your new black iron pipe with dish detergent before you put it together to get all of the oils/metal residue off to keep those contaminants from finding their way into your new vents and the boiler water. The pipe dope/tape (only use BlueMonster tape if you go the tape route) will adhere better to clean pipe as well.0
-
I'd use 2 45's (or one 45 and a street 45) and a longer nipple(maybe about 8" or so) to relocate it to somewhere in the joist bay.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements