Pressure vs. Water Test

Brando
Brando Member Posts: 11
Some contractors are ok with a pressure test of the pex tubing, some insist on running water through the loops. What are the pros and cons of this? I would like to run a pressure test because running the water supplies is beyond what I want to do at this point in the project.

As always, your thoughts are appreciated!

Brando

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,147
    The problem with an air test is that the pressure will change with the temperature and obscure small leaks, while a water test, while the pressure will also change with temperature, a small leak will be much more obvious.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • hot_rod
    hot_rod Member Posts: 22,828
    air testing is fine, especially if freezing could be possible 

    Be sure you cap off any auto air vents, they do not hold air tests