Main vents buried in finished walls

Options
Hello

So I posted previously how I wanted to insulate my pipes to improve my system and basically the near boiler piping was ripped apart. Anyway I’ve been understanding my system more and I found that the main vents have been buried in walls and ceilings for over 10 years when the previous owner had some walls put up in the basement. Somehow the Contractor did not realize he was burying vents. Long story short I was doing some renovations and uncovered them. I have no idea if they are still working. The system is terribly balanced so I suspect they are not.  I would like to do the test to hear air hissing out of them. Can anyone tell me any info about these vents and what model to replace then with.  

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,324
    Options
    They're cute. Even if they were working, they aren't meant to be main vents. How long are the mains, and what diameter are they? Then we can make suggestions for better ones.

    Also, what is that piping arrangement in the last photo? Specifically, what are the two horizontal pipes which then drop down a little ways and join together? That worries me a bit.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • bombaloo
    bombaloo Member Posts: 30
    Options
    One main is 52 feet. The other is 42 feet but has 2 extensions off it running to an addition to the house through a crawl space. The original mains are 2 inch iron. The addition pipe is 1.5 copper. I’ll add another angle but basically the 2 mains combine and the vents come off it.  
  • Jamie Hall
    Jamie Hall Member Posts: 23,324
    Options
    So am I seeing one main coming from one direction, and another main coming from the opposite direction through the wall? They both need vents on them -- but worse, the must not join like that above the water line of the boiler. They both need to go down -- individually -- to whatever wet return is lurking out of sight at the bottom of the picture. The way they are now it will be almost impossible to get a decent balance out of the system.

    Going to be a bit of a bore -- not really a do it yourself job, unless you are very handy with pipe and pipe wrenches and all -- but not that hard tor a good plumber.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    bburd
  • bombaloo
    bombaloo Member Posts: 30
    Options
    Yes they join above the water line and that single pipe goes straight down then horizontal pipe leads back to the boiler. Can you give a quick explanation of why they need separate returns until lower than the water level. I will be contacting a professional on this website. Also assuming that was taken care of what would be your suggestions for the main vents. They each have a main vent right now
  • Jamie Hall
    Jamie Hall Member Posts: 23,324
    Options
    The reason they need to drop down is to avoid having steam from one main get into the other and shut its vent before all the air has gotten out of it, making it so that any radiators on that section will be much slower to heat than the others not so trapped.

    I'd suggest a Gorton #2 for each line, but if you get a good man from this site, he may have a better idea..
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • bombaloo
    bombaloo Member Posts: 30
    Options
    Would something like this be the Solution 


  • Steamhead
    Steamhead Member Posts: 16,843
    Options
    As long as the junction point is below the boiler's waterline, yes.

    Also @Jamie Hall is correct, those cute little Hoffman #45 vents were meant to be used on convectors, not steam mains. They lack the needed capacity. Gorton #2 vents are the right choice here.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • bombaloo
    bombaloo Member Posts: 30
    Options
    Thanks. Should Groton #2 ‘s be moved up the main 10 inches or so or is it ok to have them exactly at the end of the main as these ones are 
  • Steamhead
    Steamhead Member Posts: 16,843
    Options
    10" back is preferable, but I've seen them work OK right at the end.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting