How good is good enough or do I need to add more radiation?
Jells
Member Posts: 576
So the recent cold snap was a big a challenge to a heating system as we get in NJ. It dropped to 7F in my city according to one site. The system I installed in a small apartment using it's WH and 2 K120 kickspace heaters managed to keep it to 66F. Good enough or should I add another heater under the kitchen cabs? The return water is still 120-125, plenty of heat to strip out, at least 8k BTU with a k120.
Many people would say good enough for their own home, but this is a rental. Interior temps come from a logging thermometer right by the stat set to 70.
Many people would say good enough for their own home, but this is a rental. Interior temps come from a logging thermometer right by the stat set to 70.
0
Comments
-
A rental? You may have a building code requirement to be able to maintain a set temperature -- often 70 F -- and if the space can't, the landlord may not be legally entitled to collect any rent. Talk to your building inspector.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Jamie Hall said:A rental? You may have a building code requirement to be able to maintain a set temperature -- often 70 F -- and if the space can't, the landlord may not be legally entitled to collect any rent. Talk to your building inspector.
Under the state housing codes, from October 1 to May 1, the landlord must provide enough heat so that the temperature in the apartment is at least 68 degrees from 6 am to 11 pm. Between 11 pm and 6 am, the temperature in the apartment must be at least 65 degrees.
So I only break that under the most extreme conditions.0 -
Was it a few years ago when parts of the eastern US dropped below design for a few weeks?
If you want to cover design and possibly below you need to have both enough WH and emitters
Do the kicks have multiple speed switches? What flow rate are you pumping? You could run tank temperature up also. You have 3 options for increasing output, SWT, fan speed, and flow rate.
Don't add more heat emitters then you have WH power to run. A typical gas fired WH maybe 30,000 actual output.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
hot_rod said:Was it a few years ago when parts of the eastern US dropped below design for a few weeks? If you want to cover design and possibly below you need to have both enough WH and emitters Do the kicks have multiple speed switches? What flow rate are you pumping? You could run tank temperature up also. You have 3 options for increasing output, SWT, fan speed, and flow rate. Don't add more heat emitters then you have WH power to run. A typical gas fired WH maybe 30,000 actual output.
About the noise, I've been curious to know what is the sound level of the ubiquitous PTACs found in a lot of new hi-rise apartments. Are they as loud as the ones I've experienced in motels?0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements