Putting in a main vent with limited vertical space
ybringler
Member Posts: 2
I have single pipe steam.
I have only one main vent on my system, on one side of the boiler (the longer side), right before the pipe drop into the hartford loop.
On the other side (with a shorter loop) - nothing, and I have hissing vents on the radiators as a result (pretty sure that side goes to the second floor, its all gorton 6s, new or cleaned).
It looks like there's a spot for a main vent, but the floor support cuts it off at maybe 2.5 inches.
Could I put in some angle pipes to put it off to the side a bit?
How far should I go?
Does it have to be on a slant? How much?
Will a main vent be able to be installed sideways?
The The Barnes & Jones “Big Mouth” can be installed horizontally, which might fit, but it says that that's only for Cross-over steam trap.
I have only one main vent on my system, on one side of the boiler (the longer side), right before the pipe drop into the hartford loop.
On the other side (with a shorter loop) - nothing, and I have hissing vents on the radiators as a result (pretty sure that side goes to the second floor, its all gorton 6s, new or cleaned).
It looks like there's a spot for a main vent, but the floor support cuts it off at maybe 2.5 inches.
Could I put in some angle pipes to put it off to the side a bit?
How far should I go?
Does it have to be on a slant? How much?
Will a main vent be able to be installed sideways?
The The Barnes & Jones “Big Mouth” can be installed horizontally, which might fit, but it says that that's only for Cross-over steam trap.
0
Comments
-
-
So - take off that cap, put in some small pipes etc to offset it as much as I need, and don't lose any sleep over it.
Thank you!0 -
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements