Haven't had this problem before...
Upon investigation I discovered this:
Is there any chance this could damage the pipe, and is there anything I can do to thaw it out, or should I just wait it out?
It is supposed to finally get above freezing Wednesday.
Comments
-
Probably not worth climbing on that roof to try and thaw it. We had to put frost protection on vents in cold country. Which involved increasing one size about 12” below the roof. It seemed to work to keep them from frosting. Although that looks like. 4”?
Snow shear was another problem with vents low on the pitch, however. Warm country plumbers would make that mistakeBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
In michigan I'm pretty sure increasing to 4" is required. There were about 2 days of 0f and 20 mph or so winds with light snow mixed in that I suspect is what iced this up.
You could try putting a space heater below it in the attic to see if you can warm the ci enough to thaw the ice but be very careful about how you do that.0 -
Yea it's 4". And there is no way in hell I'm climbing up on that roof. I can count on one hand with digits to spare the times I have been up there, and that was in good weather. Lol
I have full access in the attic. Was thinking a heat gun might warm it enough? Maybe?0 -
And waiting it out is always an option too isn't it? Being iced up won't damage anything at this point will it? We're supposed to hit 40 Wednesday plus rain so it should thaw quickly. Just need to remember to refill the traps in the tub and sink until then.0
-
-
-
I also have the benefit of aav's for the kitchen sink, and half bath so once the slug of water from the upstairs toilet makes it to the wye in the basement it'll be able to pull air from those.0
-
You understand the necessity of air vents.
Many people do not and wonder why all this extra pipe is installed that does nothing.
Out here in fly-over country, for the most part there is no plumbing inspection.
So in old houses there may be no vent or a badly placed one that plugs easily.
In one case the WC would not flush, just fill up to almost overflowing.
The VTR was a dry vent connected under the floor with a low heel 90.
The base of the vent was plugged with leaves etc.
A trip to the roof with a garden hose made things work.
The HO could not believe that pipe made a difference.0 -
-
Hoars frost!0
-
I think the blocked vent has highlighted another problem.
There is a sewer smell eeking out from the basement/laundry room floor drain. I bet there is break somewhere under the floor and with the vent blocked it is finding the next best place to vent.
Smells like $$$$ going out the window.
Edit: Yes there is water in the trap. first thing I checked.0 -
What other drains in the basement?
Washing machine drain....sink....etc.
Is there a plug in the floor drain clean out?0 -
If the vent is frozen it could still be burping sewer gas out through the trap. Or drying out the trap in a laundry tub or other fixture.0
-
There are rough ins for a bathroom shower, sink and toilet but they are all physically capped. The laundry sink has its own trap and the washer drains in to that sink. No other drains in the basement.0
-
Can you get into the attic with a hair dryer?0
-
Just flushed the upstairs toilet. No more suction or gurgling when flushed. It has probably opened up. The smell isn't noticeable in the basement much anymore now either.
The plumbing under the slab in the laundry room is the only original plumbing left down here. I wouldn't be surprised if it has cracked, or has separated over the past 90+ years. When ever I get a round-to-it I should bust up the floor in there and replace all of that too. Kind of sucks that the washer and dryer pad is right on top of it and is about 6" of solid concrete on top of the couple inches of slab. Lol0 -
Take the grate off of the floor drain. Often those had a clean out plug inside the basin on the side.
The bottom opening is the actual drain down into the trap.
The CO plug bypasses the trap and goes straight into the drain line for easy cleaning.
I often see the CO plug missing and sewer gas may or may not come out.1 -
This is an old clay trap. I can see the water in it. I have had it snaked out via that drain years back there is no clean out there. In fact when I had the sewer lines in the rest of the basement replaced along with a 6 ft section of the stack a clean out was added at the bottom of the stack just for that reason.0
-
Joe Listiburek at www.buildingscience.com is a proponent of basements with exterior insulated walls, footers, and floor. How about some project creep? You could do the foam board under slab insulation and pex for in floor heat.JakeCK said:When ever I get a round-to-it I should bust up the floor in there and replace all of that too. Kind of sucks that the washer and dryer pad is right on top of it and is about 6" of solid concrete on top of the couple inches of slab. Lol
0 -
WMno57 said:
When ever I get a round-to-it I should bust up the floor in there and replace all of that too. Kind of sucks that the washer and dryer pad is right on top of it and is about 6" of solid concrete on top of the couple inches of slab. Lol
Joe Listiburek at www.buildingscience.com is a proponent of basements with exterior insulated walls, footers, and floor. How about some project creep? You could do the foam board under slab insulation and pex for in floor heat.
If only I had an unlimited budget. Lol
Yea I'm not going to touch this for a long time unless something goes really wrong. The most I might do in the near term is pay someone to run a camera under that part if possible to see what has happened.1 -
The lack of venting could have sucked the water out of the trap or pushed gas through it at the laundry tub.
This is what @JUGHNE is trying to describe with the floor drain. there will be water in the trap but if someone broke out the plug to clean it and never replaced it, there will also be a hole open directly to the sewer.
You will see this:
but what is going on under the slab is this:
2 -
My floor drain does not have that.0
-
I'm guessing if you have floor drains in a basement that are connected to a sewer, especially in an older house, there's literally nothing in place for if the sewers back up?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
ChrisJ said:I'm guessing if you have floor drains in a basement that are connected to a sewer, especially in an older house, there's literally nothing in place for if the sewers back up?
Prior to rebuilding the front porch and repairing the storm lateral it was entirely possible for the runoff from my roof to infiltrate into the sanitary line. And technically it still is even now after repairing it. Allow me to explain. The collapsed storm lateral actually caused all of the soil between it and the sanitary to wash out and since both were just clay tiles it could get into it easily enough. Now as long as the sanitary continued to flow freely there was no issue. But add in some tree roots from the neighbors very large maple tree, and some, ahem, soild waste and we end up with a very effective plug. That left no where for all of the roof run off to go but one place. If you guessed my basement via the floor drain you'd be right. It also came with everything that was built up in that sanitary. Water would also came up between cracks in the floor, and from pin holes in the foundation because the footer drain was also pressurized.
Let's just say I've had a **** night before.
Now I said this is technically still possible. If the storm and the sanitary were to both get blocked, or if the sanitary got blocked and enough flushing of toilets or draining of tubs, or really any other large volume of water found it's way into the sanitary while blocked I'll end up with a similar situation.
The solution is to take advantage of the city's free snaking service. The city will come out and snake from the clean out at the side walk to the sewer main free of charge and if you sign a damage waiver they will snake up to the house as well. As long as I do this at least once a year, there is joy.
Of course I could always install a back flow preventer but those require maintenance too and in theory if the soil around them gets saturated enough it could still find its way into the basement.
Where I'm at I've never actually had an issue with the sewers mains backing up into the basement... Yet. All of my problems have been with my own runoff. The city and sewer district actually have a maintenance program where they go around with a truck and vacuum out the sewers occasionally to prevent that. The city has also been installing rention basins for storm run off, have changed the ordnances to allow downspouts to be disconnected and run on to lawns. And the sewer district has been actively hunting down cross connections between the storms and sanitarys.0 -
To be clear since I've started proactively keeping the lateral free and clear and disconnected the downspouts I have not had a problem. And now with the storm lateral repaired the footer drain and whatever still manages to get into the down spout connections can flow freely as well.
The porch getting rebuilt also stopped the leaking from there into the old coal bin as well.0 -
I've seen what a backed up sewer can do, and because of that I decided if I ever put a slop sink in my basement it's getting a ball valve on it's 1.5" drain which will stay closed unless I use it.
Unless I find a better, simpler way.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
For the most part, the floor drains here are the 1 piece as shown in the sewer cleaning picture above.
The bottom of the floor drain has a 2" FPT opening, the CO is usually 1 1/4" sometimes 1 1/2". This applies to CI and PVC floor drains.
The is a backflow device that screws into the 2" threads, it lets the water pass to the drain, but if there is any backflow of water. there is a ball that floats up to seal the opening.
For the CI as it ages the threads are pretty bunged up.
For a homemade tap, I take a 2" iron nipple and cut slots across the threads.
Hammer the ends a little to make a taper on the end to start the nipple.
This might clean the threads out to accept the PVC back flow preventer.0 -
0
-
ED, Great minds think alike!0
-
In regards to a back flow preventer on the trap, what happens at the basement shower drain, and toilet if there is one? :P sorry just being a smart ****.
0 -
JakeCK said:In regards to a back flow preventer on the trap, what happens at the basement shower drain, and toilet if there is one? :P sorry just being a smart ****.
And like I said, if I ever put a sink down there is going to have something to stop brown gold from coming in.
Ive seen exactly what happens and I don't want itSingle pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
That's assuming the "brown gold" stays in the pipe. Like I said the sewer lateral is clay, and the sewer mains are just as old. Back it up with enough pressure and it's going to ooze up through the cracks in the floors, no floor drain necessary.0
-
JakeCK said:
That's assuming the "brown gold" stays in the pipe. Like I said the sewer lateral is clay, and the sewer mains are just as old. Back it up with enough pressure and it's going to ooze up through the cracks in the floors, no floor drain necessary.
Understood.
I don't have that issue. While I do still need to cut it all out and replace with PVC, my current piping is extra heavy duty cast iron from 1910-ish.
I was planning on ripping it all out two years ago but other things came up. I'll get it done eventually.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements