Walls sweating (bad)
Ela7112020
Member Posts: 3
So we have steam heat. And we’ve been having issues with it. We think the valves are incorrect because our radiators are so noisey. They make the loudest hissing sounds.
It’s current 7 degrees here, real feel -11. And our upstairs bedrooms and ceilings are sweating bad. Currently freaking out. Is there anything we should be doing/can do to fix this?? Also we had the heat on 67 last night because of how cold it was, and it was literally kicking in every 15-20 minutes. That’s not normal?
0
Comments
-
As posted recently, some boilers run non-stop with these temperatures. Mine has not cycled since 8pm last night.
My guess is you have a leak(s). Could be chrome steam vents on the radiators, brass valves on the inlet to the radiators, or possibly the piping (least likely).
Are you losing a lot of water in the boiler? I. Other words, do you have to fill boiler more often than normal?0 -
Check your boiler pressure -- probably too high, which will aggravate any leak, and may make the vents hiss.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
Long Beach Ed said:Could just be condensation because the walls are cold too. If you have no steam leaks, are you doing lots of cooking? Lots of people in the house? Any unvented gas heaters?0
-
ScottSecor said:As posted recently, some boilers run non-stop with these temperatures. Mine has not cycled since 8pm last night.
My guess is you have a leak(s). Could be chrome steam vents on the radiators, brass valves on the inlet to the radiators, or possibly the piping (least likely).
Are you losing a lot of water in the boiler? I. Other words, do you have to fill boiler more often than normal?0 -
I suggest play detective. Look for leaking steam vents (those chrome things) and leaking radiator shutoff valves (typically have black handles). Repair or fix them all and I suspect your humidity problem will get resolved.
On the other hand, like @Jamie Hall suggested check your boiler pressure gauge. Of it reads above one pound, lower the pressure control setting.
Post photo of radiator in room above garage. Post photo of boiler pressure control (typically gray box about the size of a baseball). Post a photo of the boiler controls from about ten feet away.
0 -
The vents on steam radiators work by "trapping" steam, but letting air out. As steam rises from the boiler through the pipes, it pushes the air out of piping and radiators through these vents. Steam can't get into radiators and pipes until the air is pushed out. When steam finally fills the radiator and gets to the vent, its higher temperature closes the vent's port, trapping the steam in the radiator.
If a vent isn't closing, and it's allowing a significant amount of steam to continually escape, it must be replaced.
Lots of escaping steam will lower the boiler water level significantly and condense on cold walls. Continually adding massive amounts of fresh water to a boiler quickly accelerates its rusting and premature demise.
Of course steam leaks anywhere, as Scott mentions will have the same result. A piece of tissue or paper towel held in the path of a steam leak will turn wet. Look over the radiator, its vent and its shutoff valve. Make sure it has a vent on the end opposite the shut off valve.0 -
i agree you should so a careful inspection of the boiler and the piping to make sure there are no leaks and remember steam leaks can be hard to track down.
If the pigtail under the pressuretrol has plugged up the boiler could be running at higher pressure than it should be. High pressure will cause vents to hiss loudly, if this loud hissing just started I'd make sure that pigtail is clean.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements