Laars endurance ebp 175. Help.
ArchimoreHorie
Member Posts: 27
Hi hi I have a Laars Endurance EBP 175.
F4 and F2 codes.
Replace flow temperature sensor.
Replace high limit sensor. Boiler did work for a couple days. But now won’t work.
LCD read 181. Thanks for any help.
0
Comments
-
What does the manual say those codes mean?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Sorry for the late response.The code say. F4. Flow temperature sensor faulty.I install a new sensor0
-
Hello @ArchimoreHorie,
Since it is now apparently displaying a temperature, is it "bFt" or "tnt" or "rtt"
There are "FAULT TREE" flow charts in the manual that may help you. Does the internal pump run ?
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Bft0
-
Yes the internal pump run0
-
Hello @ArchimoreHorie,
No more Fault Codes ?
Not locked out " LO Lock Out - Combustion Related " ?
Sounds like if it is at " bFt 181 " it does not need to run, the water is at the maximum desired temperature.
Manual:
https://www.laars.com/images/uploads/products/1117F.pdf
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Yes I have a F4 codes. Replace the sensor.0
-
Boiler comes on for about 3 min then flash F4.0
-
Hello @ArchimoreHorie,
Was the wiring and connections for the replaced sensor checked all the way back to the Main PCB. Were any connectors for the sensor re-seated (boiler power disconnected).
I'm wondering if just the opposite of this is happening,
That the 'thermostatic union' is stuck closed and the heated water does not leave the boiler or another system pump is not working.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
The code does NOT say the sensor is at fault, but that there’s a flow sensor fault.
That could simply mean that sensor is doing its job and not sensing proper flow.
Is there an inlet screen? If so, has that been checked?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
The [MC] should indicate a rapid rise intemperature to 150° F (1-2 min. duration). During this period the thermostatic union at the flow outlet is closed and the boiler is operating in the internal recirculation mode. [Service note: If the temperature rise is not rapid the union thermostat may be defective and must bereplacedWill check in the morning. Also the wiring0
-
@Ironman. I don’t know if a screen0
-
Was checking my boiler now. As soon as it ignites. It goes to 220 and shut off. Any know why.0
-
It sounds like lack of flow. Plugged inlet screen or pump not functioning.0
-
I take out the heat chamber and clean it last night. Run water though it. Water flow ok. New pump0
-
Update. New pump I get after one week. Broken shaft.0
-
Broken Shaft, WoW !!! Good find.ArchimoreHorie said:Update. New pump I get after one week. Broken shaft.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements