Leaking Taco 110
speedbird
Member Posts: 27
Hi, I have a Taco 110 circulator pump feeding two toe kick heaters in the kitchen. Not the best setup, but the pump is fed by the steam boiler. I'd been lazy and hadn't flushed the loop in a while, it was filled with sludge. Needless to say, I just noticed the pump is leaking, at the seal? Maybe from a pressure build up, from cleaning the line? It's a brand new pump, only 2 years old, and I don't even run it most of the time, given I generally get enough convection circulation. Anyway, can I just replace the seal, given it's a brand new pump?
I think this is the replacement seal? https://www.supplyhouse.com/Taco-110-275RP-Taco-Sealer
I think this is the replacement seal? https://www.supplyhouse.com/Taco-110-275RP-Taco-Sealer
0
Comments
-
You can replace the bearing assembly. (the section between the motor and the pump. If this is pumping boiler water it should be a bronze pump. Iron body pumps won't last pumping steam boiler water.
You can probably replace the seal if you can find one.
A quick "fix" is to check the tension on the spring coupler, loosen the coupling on the motor end and slide the coupler towards the motor putting more tension on the spring coupler.
This puts more pressure on the seal. But be advised the quick fix probably won't last too long0 -
-
This is the easy way to replace the pump seal.https://www.supplyhouse.com/Taco-110-361RP-Bracket-Assembly-for-Taco-110-Circulator-Pump
This way is cheeper but more involved. https://www.supplyhouse.com/Taco-110-275RP-Taco-Sealer. If you look on YouTube, there are no video instructions on doing this, mostly because the low cost of the factory replacement complete bearing assembly. After spending about half for the seal only, then taking the time to replace it, then putting it all back together, then finding that the new seal leaks in a few days or a few weeks, then you get angry and hit the pump with a sledge hammer. The you need both the new bearing assembly and a motor.
After all that, most people find it easier to just get the complete bearing assembly and be done with it.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
I would change the circulator to wet rotor and put a wye strainer before the circulator. you don't need a taco 110 circulator for two toe kick heaters. Its too big and requires pretty clean water to prevent the debris from killing the seals. And steam boilers are not clean. Constant corrosion happening in a steam boiler. You will keep rebuilding this year after year.2
-
@speedbird It appears to be leaking from the 'weep" hole. You will need to apply more tension to the spring coupler. If you have any questions, please give Taco Technical Services a call during normal business hours Mon-Fri 8am-5pm EST 401-942-8000.1
-
-
-
Go with an electronic circ if you do decide to change. Save some operating $$ to offset the cost.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks everyone, very helpful. Sounds like summary is don't invest any more time/money into this pump, downsize the pump to 007, get a bronze version, and add a wye strainer.
I only see the cast iron 007? https://www.supplyhouse.com/Taco-007-F5-007-Cast-Iron-Circulator-1-25-HP-1983000-p. Can someone send link to the Bronze version?
Luckily the kitchen stays warm enough with convection flow, so I don't have to run the pump that often, unless it's a very cold day. Another downside I'd imagine of the oversized pump is it sucks that much more "sludge" out of the boiler. I'd imagine a smaller one would not do that as much.0 -
-
Had some time to work on this and stumbled across Holohan's guidance on this setup, he says three-piece pump, no strainer. Will stick with the 110 and spend $112 on a new bracket assembly, and do a better job keeping that line clear of sludge (assuming that had some impact, in addition to the acidity of the water). If it comes back, I'll spring for the stainless 110.
I did try tightening the the coupler (as tight as I could make it) but that didn't stop the leak unfort.
https://heatinghelp.com/systems-help-center/how-to-run-a-hot-water-zone-off-a-steam-boiler/0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements