Hydronic System Not Sending Heat(water) for 1 out 4 zone.

ggx
ggx Member Posts: 2
I have a GWA-105-N-T and for 1 out of the 4 zones I don't feel any heat in the baseboards of that zone.

Here is the steps I did to test:

1. I turn on the heat in my thermostat
2. I can hear the valve gear turning, then some water(cold at this point) would flow through and I also hear water flow sound for a few seconds at the baseboard.
3. Furnace would start(then stop when it reaches 180f),
4. But the hot water is not reaching the baseboards, and when I touch the pipes around the zone valve , it is lukewarm.
5. Return pipe is also cold.
6. It feels as if the zone value opened then closed by itself? Is that even possible.

Thanks

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 4,955
    This appears to be air in the closed loop. Do you know how to remove air from your baseboard loops?
    Edward Young Retired HVAC Contractor & HYDRONICIAN Services first oil burner at age 16 P/T trainer for EH-CC.org
  • ggx
    ggx Member Posts: 2
    edited November 2022

    This appears to be air in the closed loop. Do you know how to remove air from your baseboard loops?

    Thank you for the suggestion, I find this video youtube, would you say this would be the steps to follow to try?

    https://www.youtube.com/watch?v=z80WspC4Nmg