Radiant heat water temp reset?
The heat is radiant floor heating in cement slabs. The apartments have no thermostats. The water temperature is controlled by old Honeywell W964 reset controls, two zones with constant circulation, each with its own pump, controller and series 90 mixing valve actuator. The obsolete W964 controllers are acting up and unreliable.
I want to replace them with T775R controllers. I an unsure what reset curve to apply for this situation. Right now the apartments are too hot and the tenants open the windows to cool off.
This is in Chicago. The building zones are north and south with north and south exposure. Windows are newer. The building is entirely concrete.
Eventually I would also like to get a reset control on the big boiler but for now, baby steps.
There is a 100% OA Make-up Air Unit for the corridors that uses a water coil on a mixing valve so I can not turn the boiler down so low that the coil does not get enough heat.
Thanks in advance for any suggestions or assistance
Comments
-
A lot working against you there. High mass, no individual unit temperature control, a large non modulating boiler, different tenant heat needs, yikes!
Might be nice to fine a Wi Fi control that you could tweak remotely, as it may take a few tries to find a happy medium.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Yes on the zonesPeakedtoosoon said:Just to clarify.....
Two secondary mxing circuits, serving the north and south zones of the building?
All underfloor radiant heating?
The tenants have no local control of space temperature?
There is one 100% outdoor air unit for ventilation?
How many floors?
Do you know what the radiant design flow and return temperatures are?
Yes, all apartments are in floor radiant copper in cement
No, tenants have no thermostats. Maybe in the future but not now.
Yes, the MAU on the ground floor has a fan coil heater for the room and the MAU has a hot water coil to maintain 70° air
25 floors
I do not know what the design return temp is. The building was constructed in the 1970's and those design factors have been long lost in the decades.R2B4BTU0 -
Good idea but for now I just want to propose a modernization of the old Honeywell controllershot_rod said:A lot working against you there. High mass, no individual unit temperature control, a large non modulating boiler, different tenant heat needs, yikes!
Might be nice to fine a Wi Fi control that you could tweak remotely, as it may take a few tries to find a happy medium.R2B4BTU0 -
Tekmar and HBX are a couple popular choices, add the remote access later if you need.
https://hbxcontrols.com/cpu-0550.phpBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Interesting. I will look further into that. One thing is this is a mixed/low income co-op building that still has a lot of issues to overcome. I will be returning to check the pilots & burners. Replace the MAU filters and leave more filters for the maint crew to change. Replace the zone pumps J5 coupler sleeves and one looks to be out of alignment. Replace the broken actuator linkage on the MAY mix valve. They don't have the money for huge upgrades all at once. I will try to explain that the efficiency gains would pay for themselves. Those old atmospheric boilers with their 36" stacks dump enough heat to supply another building!R2B4BTU0
-
So is there a basic setting you would recommend to start with using a T775R?
Min temp at warm outdoors like 70° water at 70° and Max temp at design like 110° water at 0° ? with a night time setback of 5° ? All the info sounds great and I know it can be a bit of a crap shoot at times but I gotta start somewhere.R2B4BTU0 -
@ Peakedtoosoon The building is 25 stories all concrete. Just looking for a starting point. It controls by mix valve discharge temp.R2B4BTU0
-
Zone sensors are a nice idea but it's not going to happen
R2B4BTU0 -
Usually 68- 70F is a starting point, the high temperature if it is slab radiant? may be 110- 115. Floor covering makes a difference, if carpet is over the slab, SWT may need to be higher.ottostingray said:So is there a basic setting you would recommend to start with using a T775R?
Min temp at warm outdoors like 70° water at 70° and Max temp at design like 110° water at 0° ? with a night time setback of 5° ? All the info sounds great and I know it can be a bit of a crap shoot at times but I gotta start somewhere.
Without any design, maybe start with the settings that are currently dialed into the HW?
With the HBX or tekmar, you have room to grow the control system, if zoning is added or you want online capability. Wireless zoning is another option down the road. Start with the basic control, add as $$ allows.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Thank youR2B4BTU0
-
A bit of looking into the existing controller. I will try the 2.5:1 reset ratio with the recommended -25 Parallel shift. That will give me a 55° water temp at 70° and a 2.5:1 rise.
Thanks for he advice. I will look into the HBX. If we're going to upgrade, we might as well have options for future add on control. It all comes down to their budget and my sales skills.R2B4BTU0 -
-
So on a 0 day you sent 175 to the slab? That seems awful high. 1- 1.5 seems more in. Line with slab reset.ottostingray said:A bit of looking into the existing controller. I will try the 2.5:1 reset ratio with the recommended -25 Parallel shift. That will give me a 55° water temp at 70° and a 2.5:1 rise.
Thanks for he advice. I will look into the HBX. If we're going to upgrade, we might as well have options for future add on control. It all comes down to their budget and my sales skills.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
WHY?ottostingray said:Zone sensors are a nice idea but it's not going to happen
0 -
pecmsg said:
Zone sensors are a nice idea but it's not going to happen
WHY?R2B4BTU0 -
I think at some point the discussion with building owners with buildings like that is $$. If you want to go that far with them? I'd get past fuel bills and show them where zoning could save some big fuel consumption costs, and increase tenant comfort.
As fuel costs continue to rise, the concept of building upgrades, heating system upgrades makes more and more sense.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements