Tigerloop
Egreenbuilt
Member Posts: 2
in Oil Heating
I installed new tank with overhead line and tigerloop. System starts fine after bleeding, runs for 12-16 hours and slowly runs out of fuel. Tank is full, filter and all components are new. No signs of leaks or air bubbles in the tiger loop. Line is 35' long, rises 6' at the tank, and drops 7' at the boiler. it has done this 3 times.
0
Comments
-
Did you install the oil pump by-pass plug?0
-
Hey Jon, no I did not, just did a quick google search, says its a 1/16" NPT plug that go's in the 1/4" return port. Is that correct?
Thanks
0 -
-
Only get the OEM bypass plug for that Beckett/Suntec A pump.
What make and model burner is that? What's the pump pressure.
Is that Clean Cut pump OEM to the burner? What primary is being used?0 -
Yes, That is correct. The Suntec plug is installed with an allen wrench. Any 1/16 plug will do the job as long as you can screw it in. The allen wrench type makes it easy.Egreenbuilt said:Hey Jon, no I did not, just did a quick google search, says its a 1/16" NPT plug that go's in the 1/4" return port. Is that correct?
ThanksEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Running the pump WITH the bypass plug installed can ruin a pump unless you have a return ie, a 2 pipe system. It's also why I never liked valves on the return. Start the pump with the valve closed and instant shaft seal blown, except riello pumps have such a good seal it will stall the motor and not rupture the seal. Running the pump without a bypass plug does no harm, on a two pipe system won't hurt the pump but it is likely to become air bound. With a tigerloop you do need the bypass plug installed.0
-
-
You got that backwards. Running a 2 pipe system with no bypass plug is not going to blow a pump seal. It just will not be self priming.Dave Carpentier said:They saying running without the bypass plug installed can wreck the pump seals.
You might be looking at buying a pump soon (or now).
Running a single pipe from the oil tank with a bypass plug installed will cause a pump seal to fail, because there is no place for the unused oil from the gear set to go if the bypass is plugged and the return port is also plugged. Hydraulic pressure can be very strong and something has got to give. The pump seal is the weakest link
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Doh! I knew it was something caused something.EdTheHeaterMan said:
You got that backwards. Running a 2 pipe system with no bypass plug is not going to blow a pump seal. It just will not be self priming.
Apologies to the OP if I caused a moment of panic.
30+ yrs in telecom outside plant.
Currently in building maintenance.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements