Setting up new thermostat

Fmassarotto_9
Fmassarotto_9 Member Posts: 148
edited November 2022 in Thermostats and Controls
I need advice on how to program my new honeywell thermostat RTH6360D. It appears the way i have it set causes it to cycle multiple times causing it to overheat. What would be the proper setting for a steam boiler with radiators beginning on page 8 and 9?

https://www.honeywellstore.com/store/images/pdf/rth6360d-5-2-programmable-thermostat-manual.pdf

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,401
    edited November 2022
    Have you set parameter 200 is on 3 and 205 to 12 in the setup menu?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,401
    Also, How many wires are you using?
    Did the old thermostat operate the heating boiler only?
    Did your old thermostat operate both a boiler and a air conditioning system?
    What position is the R micro switch set, up or down?
    Are you using the common (C) wire?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Fmassarotto_9
    Fmassarotto_9 Member Posts: 148
    Also, How many wires are you using? Did the old thermostat operate the heating boiler only? Did your old thermostat operate both a boiler and a air conditioning system? What position is the R micro switch set, up or down? Are you using the common (C) wire?
    Just W and R wire, only heating, 
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,401
    edited November 2022
    OK. Then it should just be a matter of the setup process.
    Press and hold MENU and + for about 5 seconds to enter the program menu

    Press Select to open the setup menu

    Press Select to scroll thru the number options
    You can set the clock and setback options you want to use

    When you get to option 200, set it to option 3 using the + or - buttons
    then press select to lock in your selection
    when you get to 205, set that for option 12 using the + or - buttons
    then press select to lock in your selection

    Once you get to the end of the menu the display will read DONE
    Press select to lock in your changes

    The important numbers for steam are 200 = 3 and 205 = 12
    The rest of the numbers are up to your preference.

    If you have already completed this setup, then let us know. If that does not solve, then there is a wiring problem.

    EDIT: also important is the R micro switch on the wiring sub-base. That switch should be up




    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Fmassarotto_9
    Fmassarotto_9 Member Posts: 148
    OK. Then it should just be a matter of the setup process. Press and hold MENU and + for about 5 seconds to enter the program menu Press Select to open the setup menu Press Select to scroll thru the number options You can set the clock and setback options you want to use When you get to option 200, set it to option 3 using the + or - buttons then press select to lock in your selection when you get to 205, set that for option 12 using the + or - buttons then press select to lock in your selection Once you get to the end of the menu the display will read DONE Press select to lock in your changes The important numbers for steam are 200 = 3 and 205 = 12 The rest of the numbers are up to your preference. If you have already completed this setup, then let us know. If that does not solve, then there is a wiring problem. EDIT: also important is the R micro switch on the wiring sub-base. That switch should be up

    alright, the setting were way different, i'll see how it goes !