Increasingly wild pressure fluctuations as hydronic system increases temperature

13»

Comments

  • MikeAmann
    MikeAmann Member Posts: 1,044
    While you are working on the plumbing is the time to add these convenience items, exactly as you suggested.
  • hot_rod
    hot_rod Member Posts: 23,036
    No reason why not to add service components
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Ironman
    Ironman Member Posts: 7,508
    The dirt mag doesn’t require disassembly like a strainer does: you simply blow it down at the drain port. There’s no strainer in it, just a coalescing media.

    But if you wanna add valves, have at it.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    mattmia2
  • hot_rod
    hot_rod Member Posts: 23,036
    We did have a larger size DirtCal that was returned with flow complaints. It had a brown cotton glove stuck against the media
    I have also seen them jammed with Teflon tape shards
    I consider both of those to be operator/ installer error

    but had not the DirtCal stopped the junk, a pump or boiler opening may have😖
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2Brent H.
  • mattmia2
    mattmia2 Member Posts: 10,682
    I guess there is the question why is it so filthy. Is there or was there glycol in this that hasn't had the inhibitors maintained?
  • np_mdbr
    np_mdbr Member Posts: 82
    @mattmia2 I'm pretty sure the previous owners were adding tap water to the system via the reserve tank. I checked the composition with a refractometer and the freeze tolerance was pretty bad (around 28F). Since then, I have replaced about 20 gallons of fluid with brand new fluid and the tolerance is now around 2F.
  • mattmia2
    mattmia2 Member Posts: 10,682
    Glycol as provided from the factory has corrosion inhibitors in it. There are test strips to test the effectiveness of those inhibitors. If they are depleted it will corrode things badly. You should test it and add an inhibitor package or change the glycol mix.
  • hot_rod
    hot_rod Member Posts: 23,036
    Mixing glycol with tap water compromises it, depletes part of the inhibitor package, as it tries to “fix” the tap water undesirables.
    Maybe check and add a squirt of inhibitor boost. Test kits give you a good idea, a better analysis would be sending a sample to the manufacturer.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2