Wait, what?

HVACNUT
HVACNUT Member Posts: 6,329
I showed up for a heat maintenance this morning and saw the PVC elbow with the plug. I've been servicing the gas furnace with AC in the attic for a few years now and don't remember ever seeing the PVC. I asked the client "what's up with that?". He said he had his basement finished and the PVC was a failed inspection location for the vent on the sewage ejector, so the plumber  had to relocate it. Ok, cool.
I go into the attic to do my thing. While doing the test with the analyzer, I look around and see this.The contractor Tee'd the sewage vent into the furnace exhaust at the concentric venting. My brain first said "its April fool's day". Then I realized its Halloween and got a trick instead of a treat.
Needless to say I shut the power and turned off the gas to the furnace. Recommended a plumber. 
There were permits pulled for the job so I don't know how it was missed. And I usually have tunnel vision anyway, forget first call on a Monday morning, so I'm glad I saw it. 
I'm no chemist, but what would happen if the exhaust gasses mixed heavily with sewage fumes? Pretty noxious I bet.

Zman

Comments

  • Paul Pollets
    Paul Pollets Member Posts: 3,663
    Competence reigns supreme...
  • pedmec
    pedmec Member Posts: 1,066
    Thats why we had a code change in mass and required all power vented or direct vented piping be labeled.
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Yikes. What's the insulation supposed to be doing?
    If he ran the pipe that far, wasn't much more work to punch it thru the roof.

    There was an error rendering this rich post.

  • ChrisJ
    ChrisJ Member Posts: 16,315
    edited October 2022
    pedmec said:

    Thats why we had a code change in mass and required all power vented or direct vented piping be labeled.

    If the equipment is a few feet away like in the situation above, do you really feel a label is going to fix or improve that situation?

    Labels aren't going to fix incompetency.
    You can have all of the labels and codes you want and it's not going to help if the people following them are like whoever did the work mentioned by the OP.

    I have to admit @HVACNUT this is one of few posts on here that actually made me laugh out loud.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    mattmia2Alan (California Radiant) Forbes
  • KC_Jones
    KC_Jones Member Posts: 5,840
    I have a friend who had bathroom vent fans installed, they hooked them up to the DWV vent system in the attic. I found it by accident when I was doing some other work for him.

    The OP's situation. I mean I have no words, everything was in the same area, that pipe is obviously going to the furnace. That's a whole new level of stupid, like they should 100% not be in any trade level of stupid.

    Can't people lose their license for this?

    As a homeowner I would have been making a lot of calls to contractor and inspector. Heads would be rolling right now.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • pedmec
    pedmec Member Posts: 1,066
    @ChrisJ Its not for guys like us. i would say its for the do it yourself. i think if it wasn't happening over and over again you probably wouldn't need stickers but what would i know. I guess your just smarter than everyone else and never make mistakes
  • ChrisJ
    ChrisJ Member Posts: 16,315
    pedmec said:

    @ChrisJ Its not for guys like us. i would say its for the do it yourself. i think if it wasn't happening over and over again you probably wouldn't need stickers but what would i know. I guess your just smarter than everyone else and never make mistakes


    Absolutely I make mistakes. All of the time.

    On a separate note..


    How did it fail the first time and the inspector didn't catch that the 2nd time? Wouldn't the first failure have been kind of a red flag?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 10,924
    Inspector didn't want to go in the attic.
    PC7060GGross
  • Steamhead
    Steamhead Member Posts: 17,380
    KC_Jones said:

    I have a friend who had bathroom vent fans installed, they hooked them up to the DWV vent system in the attic. I found it by accident when I was doing some other work for him.

    The OP's situation. I mean I have no words, everything was in the same area, that pipe is obviously going to the furnace. That's a whole new level of stupid, like they should 100% not be in any trade level of stupid.

    And, once again- you can't fix stupid!
    KC_Jones said:

    Can't people lose their license for this?

    As a homeowner I would have been making a lot of calls to contractor and inspector. Heads would be rolling right now.

    You should, and they should.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • They walk among us.

    "They're both vents. Why not combine them?"
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    GGross
  • Danny Scully
    Danny Scully Member Posts: 1,440
    Guys need to learn the air admittance valve trick with sewer ejectors…a lot of wasted work to only do it wrong lol. 
    ChrisJPC7060
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,470
    Ma has required that flue and air intake pipes be labeled for quite a few years now as @pedmec pointed out.

    I thought it was a stupid requirement and it is but I have heard so many stories of people cutting and teeing into flue or intakes that I can understand why it is reuired.

    Same goes for the electrical code. It never said you COULDN't mount a electrical panel on a ceiling .....until someone did it
  • HVACNUT
    HVACNUT Member Posts: 6,329
    Guys need to learn the air admittance valve trick with sewer ejectors…a lot of wasted work to only do it wrong lol. 
    I'm not sure a Studor vent is permitted. I didn't ask. Town of Brookhaven NY. You'd think it was the easiest solution, but obviously nobody thought much of anything. What did Moe say, "I keep tryin' to think, but nuttin' happens."
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    HVACNUT said:


    ...What did Moe say, "I keep tryin' to think, but nuttin' happens."

    I think Curly said that...lol


    There was an error rendering this rich post.

  • HVACNUT
    HVACNUT Member Posts: 6,329
    ...What did Moe say, "I keep tryin' to think, but nuttin' happens."
    I think Curly said that...lol
    Yes, Curly. I only had one cup of coffee when I wrote that.
    PC7060
  • HomerJSmith
    HomerJSmith Member Posts: 2,635
    Works for me!
  • ChrisJ
    ChrisJ Member Posts: 16,315
    This one was Moe


    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    MikeAmann