Newbie to Steam Heat
mgambuzza
Member Posts: 29
Just bought our 1891 home which has a boiler (Utica PEG300CDE). Working through some of the kinks such as defective/missing vents, leaking spuds, mud/muck coming when draining the boiler, and unusually, the upper floors colder than the lower. Flushed the system a number of times and looks better. More of the radiators functioning properly. In the basement, I was wondering about a couple of the main air valves in the basement. The one in the picture circled in Green is a Hoffman No6, the other circled in Red is one I couldn't easily identify as the marking are faded. I've included individual snapshots of them. I was wondering if these would affect performance and cause good pressure to not get to all my radiators. BTW - my pressure gauge has consistently read zero (pigtail and new gauge on order). Look forward to responses.
0
Comments
-
Here's the other unit circled in Red
0 -
First don’t focus on pressure in steam heating, you don’t want it, it’s bad. Pressure in steam heating is back pressure of the system not allowing the steam to go where it wants.
As far as the vents, if they are working they are woefully inadequate. The red one shouldn’t be there, it’s on the header and is doing nothing in that position. Vents should be in the vicinity of the end of mains.If you are looking to replace/upgrade them, let us know how long and what size the mains are and we can recommend an appropriate amount of venting.
Also, in case you aren’t aware, that boiler is not piped properly.1 -
Hello @mgambuzza, The vent circled in Red may be a pressure relief valve from a previous boiler setup.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
The thing in red looks like some sort of ancient relief valve leftover from the old boiler.0
-
Hello @mgambuzza, To better clarify, the vent that was circled in Red may be a pressure relief valve from a previous boiler setup and there may be a second Main Vent in the background of this picture. The first Main Vent was in the Green circle of another photo.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
-
More pictures needed of the boiler, its near piping from different angles and the other pipes in your basement.0
-
Hello @mgambuzza,
You could, but why bother ? If it is not leaking I would just leave it alone, why ask for trouble.mgambuzza said:One circled in red, the potential vintage pressure relief valve, would it be safe to say I could remove that and cap it off??
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements