Moving to continuous circulation with TRVs
The goal was to have better control over the room temp in different parts of my house.
I realize now, that a variable speed circulator should be used given the changing demand, and since I do not have a pressure-activated bypass.
I am going to be installing an Alpha2 15-55F to replace the existing UPS 26-99 FC. Head=7.75, Flow = 10.2 GPM.
My boiler is the Weil Mclain 97+ 155 (https://www.weil-mclain.com/sites/default/files/field-file/wm97-ct-manual_1.pdf)
Currently, the circulator starts to run when there is a call for heat.
My question: how do I get the circulator to run continuously during the heating season?
Also, am I on the right track?
Comments
-
You are. There are a number of control strategies to do this sort of thing, but if all the heat is basically controlled by the TRVs, perhaps the best -- if your boiler will allow it -- is to run the boiler continuously, or nearly so, off an outdoor reset curve, and run the circulator any time the boiler water is warm enough.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thanks, I should add my boiler is piped with primary/secondary with DHW having priority.
My house has a high demand for DHW a few times a day, which results in the boiler switching over to DHW, the circulator stopping, and then starting up again when the DHW call is satisfied.
I would like the circulator to be always operating even during DHW calls.
0 -
Why? All that will accomplish is slow down recovery for the DHW.skiereric said:Thanks, I should add my boiler is piped with primary/secondary with DHW having priority.
My house has a high demand for DHW a few times a day, which results in the boiler switching over to DHW, the circulator stopping, and then starting up again when the DHW call is satisfied.
I would like the circulator to be always operating even during DHW calls.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
How is the indirect piped and pumped? With enough boiler power, and adequately sized pump and piping, you should recover the DHW quickly, 10- 20 minutes.
It depends on incoming water temperature, size of tank, recovering while still running DHW, etc.
Lowering the dhw load may help, lower flow shower heads? stagger dhw loads.
Raise the indirect operating temperature and add a mix valve, for more drawdown.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Trying to avoid the sounds that occurs from the pex flexing against the floors/studs when the circulator first starts up. After a minute or two after the circulator starts up it is completely silent.Jamie Hall said:
Why? All that will accomplish is slow down recovery for the DHW.skiereric said:Thanks, I should add my boiler is piped with primary/secondary with DHW having priority.
My house has a high demand for DHW a few times a day, which results in the boiler switching over to DHW, the circulator stopping, and then starting up again when the DHW call is satisfied.
I would like the circulator to be always operating even during DHW calls.
0 -
hot_rod said:
How is the indirect piped and pumped? With enough boiler power, and adequately sized pump and piping, you should recover the DHW quickly, 10- 20 minutes.
It depends on incoming water temperature, size of tank, recovering while still running DHW, etc.
Lowering the dhw load may help, lower flow shower heads? stagger dhw loads.
Raise the indirect operating temperature and add a mix valve, for more drawdown.
Yes, the call for DHW takes no more than 10 minutes. What is annoying, is that I hear the creaks of the pex against studs/flooring whenever the circulator starts up, this lasts for 1 minutes or so any then becomes silent.
0 -
Kind of a tradeoff there, isn't it? Either the annoying sound -- or much longer recovery (perhaps in the hours) for the domestic hot water.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Actually the expansion tank connected at the inlet of #5 circulator would establish a nice PONPC for all those circs.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I have some experience with trying to correct this. The creaky pex thing is a result of temperature change, not flow. I failed at trying to quiet a creaky staple-up job by having the pump run longer at a greater temperature delta. When it was time to bring the RFH up to temp though, the pex creaked away. There's a solution to the noise in every case but my guess is this isn't going to get it done for you and you might want to to reassess the situation.skiereric said:
Trying to avoid the sounds that occurs from the pex flexing against the floors/studs when the circulator first starts up. After a minute or two after the circulator starts up it is completely silent.Jamie Hall said:
Why? All that will accomplish is slow down recovery for the DHW.skiereric said:Thanks, I should add my boiler is piped with primary/secondary with DHW having priority.
My house has a high demand for DHW a few times a day, which results in the boiler switching over to DHW, the circulator stopping, and then starting up again when the DHW call is satisfied.
I would like the circulator to be always operating even during DHW calls.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
figure 57 is the wrong diagram as that is zoning with circulators. figure 54 is a better depiction of what you have. trv's are zone valves.0
Categories
- All Categories
- 85.9K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 78 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 94 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 59 Pipe Deterioration
- 886 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 51 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements