STEAM BOILER OVERFLOW TRAP
Weil
Member Posts: 23
In piping multiple steam boilers, the manufacturer requires a trap to be installed 4 inches above the water line and piped to the boiler feed tank to prevent the flooding of the dormant boiler. I have seen both F&T's and bucket traps specified. Which is proper?
0
Comments
-
Could the buckets lose their prime and pass steam?0
-
The few that I have seen have been F&T traps.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0 -
Two boilers, both have F/T traps. One or both have failed, steam blowing out tank vent pipe.
0 -
can you feel the outlets for steam hot ?
looks like the one on the left drops down to the wet return, not that that couldn't be it, but,
the one on the right pipes to the air vent already,
I would rebuild them both,
consider getting the Ptrol piping up out of the water,
dirty water ?known to beat dead horses1 -
High Level Spill traps are usually ¾” F&T traps. As Neilc says, rebuild them both.
Here's an interesting old thread on the subject of multiple boiler connections if you have the time:
https://forum.heatinghelp.com/discussion/186553/multiple-steam-boiler-piping-designs0 -
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements