wet return with F& T traps?
plumb1pa
Member Posts: 10
Just visited a customers house with a one pipe system and a wet return, but there were Wye strainers and steam traps at the end of both mains. Been there for 20 plus years now the boiler return water is not getting back to the boiler quick enough. Do I need the F & T traps? I will be cleaning the Wyes. Thanks for any input
0
Comments
-
Probably not, but one would have to look at the elevations of the steam mains relative to the boiler, and be sure that the wet returns are, indeed, wet. That said, the system should drain condensate by gravity, and steam would be kept out of the returns simply by gravity. I would be a bit cautious about the strainers, too -- there really shouldn't be anything in the condensate to strain.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
After 20 years the F&T's could be clogged with sludge as are the strainers.
Quick and easy test would be to open the F&T's and strainer, clean them out and then remove the guts from both. This would be about the same as a run of pipe.
What is there for steam main air venting?
If there are extra plugs on the F&T, you could add air venting there if needed.
This would avoid pipe work over.0 -
That seems really odd. If you have a wet return whats the purpose of the f&t? It really doesn't help as the condensate in the return has to stack higher to get the condensate back into the boiler.
Is the wet return underground? I'm wondering if you have a leak in the return and they added the f&t to prevent the steam from getting back to the boiler instead of repairing the leak. I know it sounds crazy but so is adding a f&t on a one pipe.
Was there a condensate pump in the boiler room? trying to think out of the box here, lol
0 -
You don't need F & Ts unless you have a condensate pump0
-
Some old Vapor systems did use F&T traps on steam main drips. In these systems the return was "non-pressurized" and the returning condensate often went through a Return Trap. I've seen Webster systems set up this way.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements