Changing to a TVR valve on a Cast Iron radiator
Vulcanspotter655
Member Posts: 2
I want to change the valves on the cast iron radiators for TVR valves which I have purchased. There are shut off valves on the same run of pipes going to the radiators in the same room.
My question is how do I change them?
My question is how do I change them?
0
Comments
-
what kind of connections does your new TRV have/ kind of makes a difference in how it might be done.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Looks like that one is already bushed down to 3/4" NPT? Most valves are 3/4, angle or straight, just watch flow direction.
There are valves known as convertible, where the knob removes and an adaptor and actuator can be added. Is there a brand name on that valve, it may be able to have a thermostatic head added.
Here is an example of a valve that I added a pex connection onto. It is a convertible valve, remove the cap and add the head.This would go onto the return end of the radiatorBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The plastic pipe clips and bent copper, I'm thinking UK or Ireland...just a guess.
There was an error rendering this rich post.
0 -
Hi I live in the UK. I've bought replacement valves from ebay so I lot cheaper than from a supplier.0
-
Interesting looking valve, install as shown in the pic. Is it a name brand, or a knock-off? Sometimes the bargain products are copies of a quality name brandBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
It looks like maybe the new one is the same manufacturer as the existing one in which case the spud nut may have the same threads.
If so, your job just got easier: Drain the system to just below the radiator, undo the spud nut, spin off the old valve, screw on the new valve and tighten the spud nut. Pressure test for leaks.
If not the same threads, you will have to remove and replace the spud to the radiator.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements