Pilot light goes out when gas valve opens
Sethamin
Member Posts: 60
I have a gas-fired steam boiler which now won't light when you call for heat. The pilot light is on, but then as soon as the main gas valve opens the pilot light goes out. Actually, the pilot light doesn't totally go out, because it comes back once the gas valve closes. But presumably it gets too small to actually light the boiler (maybe it would light if I let it sit there with the gas on for a long time, which I don't want to do).
My best guess is that the pilot light tube is clogged and there's a pressure drop when the main valve opens that is enough to almost put the pilot light out. Would cleaning or replacing the pilot tube fix that? Or might it be the combination gas valve? Any ideas for how I could narrow the problem down more? Boiler is 20+ years old, and I've never had any problem with the pilot light before (save for a bad thermocouple once). Any tips appreciated.
My best guess is that the pilot light tube is clogged and there's a pressure drop when the main valve opens that is enough to almost put the pilot light out. Would cleaning or replacing the pilot tube fix that? Or might it be the combination gas valve? Any ideas for how I could narrow the problem down more? Boiler is 20+ years old, and I've never had any problem with the pilot light before (save for a bad thermocouple once). Any tips appreciated.
0
Comments
-
Time to call a pro. This can be a dangerous situation.
If there is enough gas pressure to feed the pilot until the main burner kicks on, your gas supply is restricted in some manner. Have a pro check the incoming gas pressure with the main burner off and then on. If the problem exists on all gas appliances, there is an issue with the service piping and/or meter, for which you'd need to call the gas supplier.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
-
Is it natural gas or propane? Is there enough gas in the tank if it is propane?0
-
Turns out it was the combination gas valve that was the problem. Likely some debris got stuck in there and was causing an obstruction. Replaced it and everything is good now.0
-
Sethamin said:Turns out it was the combination gas valve that was the problem. Likely some debris got stuck in there and was causing an obstruction. Replaced it and everything is good now.Where’s the sediment trap?
lines properly sized.Something is Wrong!0 -
did a professional with combustion analysis equipment that knows how to use it replace and adjust the new valve?0
-
Yes, I had my HVAC company properly replace it.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements