C wire & Aquastat L8148E with 3 zones

Royals
Member Posts: 13
I would like to use 2 NEST thermostats on my boiler. I have a Honeywell Aquastat L8148E. I also have 3 Zones (valves are Honeywell V8043E1012) and will be using a NEST on only two of the Zones
I have currently 2 wires connected to the thermostats, both plain 'speaker' wire not colored wires.
Anyone care to help with getting 'C' Wire to the two NEST thermostats maybe with wire diagram ?
Thank-you
Royals
I have currently 2 wires connected to the thermostats, both plain 'speaker' wire not colored wires.
Anyone care to help with getting 'C' Wire to the two NEST thermostats maybe with wire diagram ?
Thank-you
Royals
0
Comments
-
Do the zone valves have a separate transformer?
Do the zone valves use the transformer in the L8148E?
This will determine where to get the C wire from.Edward Young Retired HVAC Contractor & HYDRONICIAN Services first oil burner at age 16 P/T trainer for EH-CC.org0 -
I am pretty sure the zone valves have separate transformer, outside the Aquastat, let me just confirm0
-
So Yes i can confirm, there is an extrenal transformer, so from the external transformer, the yellow wire goes near the Zone valves, and is then spliced to the 3 zone valves one of their yellow wires (they have 2 yellow wires on each valve). The blue wire from the external transformer, goes to near the Zone valves and is spliced, to the 3 thermostats wires, then from there on to the 2nd yellow wire on their respective zone valves. The 2 RED wires from the Zone valves then go to Aquastat, one each to T and TV.
Make any sense ?
Royals0 -
Then the C wire on the thermostat goes the the C of the zone valve transformer. diagram to followEdward Young Retired HVAC Contractor & HYDRONICIAN Services first oil burner at age 16 P/T trainer for EH-CC.org0
-
Thank-you , which wire would be the 'C' on the valves that i can connect the Themostat C wire to?EdTheHeaterMan said:Then the C wire on the thermostat goes the the C of the zone valve transformer
0 -
-
To add a note to @EdTheHeaterMan 's excellent diagrom (wish i could draw like that) -- there is no connection where the black/yellow vertical crosses the black horizontal...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Ed: I can't thank you enough. everything working like it should. The diagrams were perfect and I followed them easily.EdTheHeaterMan said:
C on the valve is one of the yellow wires.
W on the thermostat is the other yellow wire
Thanks Jamie. I cleaned up the connections and added "wire nut dots"
You're the best
Royals1
Categories
- 120.1K All Categories
- 83.6K THE MAIN WALL
- 2.8K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 414 Carbon Monoxide Awareness
- 29 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.6K Gas Heating
- 114 Geothermal
- 151 Indoor-Air Quality
- 2.9K Oil Heating
- 49 Pipe Deterioration
- 734 Plumbing
- 5.2K Radiant Heating
- 355 Solar
- 13.8K Strictly Steam
- 3K Thermostats and Controls
- 50 Water Quality
- 36 Industry Classes
- 69 Job Opportunities
- 14 Recall Announcements