New install - how’s the piping look?



Comments
-
-
I also like the Vent Connector piping. Nice and shiny.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Seriously, The piping looks pretty. However look at this photo and look at figure 12 and table 5 from the instructions.
Compare the pipe sizes in the manual to the pipe sizes you actually have, then ask yourself how you think the piping looks.
It might work just fine, but if it doesn't, you know where to start looking.
Best of luck!
Respectfully submitted,
Mr.Ed
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
My comments are not intended to offend, or criticize work that is well done. We all started somewhere and my first boiler install was not the prettiest thing you ever saw. But it worked because I had some help from experienced installers. (on the second day) We all learn better ways to do stuff each and every day.
I'm wondering why none of the other steam experts have not chimed in... Because no one wants to hurt anyones feelings on purpose. If you have a problem that is associated with "wet steam" and come here to find a solution, there will b many that will point out the pipe size issue. But since we don't know if you will even have a problem, then better to stay silent.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
Just saw this. @oldsteamer , the steam pipe size above the reducing fitting coming out of the boiler is, according to the manual, too small. It looks like 2-inch where the manual says 2-1/2". This can cause wet steam, banging and reduced efficiency. It also may mean that if the boiler develops an issue during the warranty period, W-M may not honor the warranty since it was not installed the way the manual specifies.EdTheHeaterMan said:.......I'm wondering why none of the other steam experts have not chimed in... Because no one wants to hurt anyones feelings on purpose. If you have a problem that is associated with "wet steam" and come here to find a solution, there will b many that will point out the pipe size issue. But since we don't know if you will even have a problem, then better to stay silent.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
-
-
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System2 -
Check the edr of the boiler vs the edr the installer calculated from measuring your radiators too. The reason the header is too small for that boiler could be that the boiler is too large for the connected radiation and it will run very short cycles.0
-
As other have stated should have followed the installation instruction set piping sizes they are a minimum . The installer just did 2 inch as to not have to redo the 2 takes which would not have been much work or money .As it may seem to work fine but as always said steam is quite forgiving and it usually takes a lot of knuckle heading to get to the point where it doesn’t work but that takes a lot of stupidity or cheapest one or the other maybe both . I would have lost most of my faith in the installer for not adjusting the pressuretroll which any semi seasoned steam boiler installer would lower prior to start up . Also the boiler should have been cleaned through either just skimmer or the real deal which would be wanding the boiler out from the bottom and then refilling steaming and skimming without that being done any faith I had was surely spent praying . I have seen much worse but I would ask the installer about not following the manafactures piping specs ?
Peace and good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0 -
-
Proper piping results in drier steam, which contains more usable heat per pound than wet steam.
https://tlv.com/global/US/steam-theory/wet-steam-dry-steam.html0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements