Taco SR504-4 switching relay - first relay makes noise or drops on certain zones
criocin
Member Posts: 5
Hello,
I have 3 zones on a Taco SR504-4 switching relay. One is on Nest with the AC and the other 2 are on Sensi.
When I turned on the heat on the Nest the first relay ( the one not related to the zones) started to drop here and there (maybe when the pump started?). I disconnected the AC from the Nest and now it does not drop anymore but it sounds that is about too (makes noise).
When I turn zone 2 which is on Sensi the relay makes a lot of noise but it does not drop.
When I turn zone 3 which is on Sensi the relay makes no noise.
I can't figure this out. I think is a bad relay which I don't think it can be changed individually. I might have to replace the entire Taco switching box.
Looking for advice.
Thank you
I have 3 zones on a Taco SR504-4 switching relay. One is on Nest with the AC and the other 2 are on Sensi.
When I turned on the heat on the Nest the first relay ( the one not related to the zones) started to drop here and there (maybe when the pump started?). I disconnected the AC from the Nest and now it does not drop anymore but it sounds that is about too (makes noise).
When I turn zone 2 which is on Sensi the relay makes a lot of noise but it does not drop.
When I turn zone 3 which is on Sensi the relay makes no noise.
I can't figure this out. I think is a bad relay which I don't think it can be changed individually. I might have to replace the entire Taco switching box.
Looking for advice.
Thank you
0
Comments
-
-
Hi
My guess, it is not the control. An easy test is to disconnect the thermostats and place a simple jumper across TT terminals to see if it still makes noises, or act erratically.
Some of these power robbing thermostats require more voltage than the control has available. I would check with Taco tech support at 401-942-8000. They are better equipped to answer these questions when attempting to trouble shoot a problem.
I’m curious to know how you make out.
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions1 -
criocin, as Joe suggested I would disconnect the t-stat going to your SR control and jump the R-W on the control to see if the issue is still there. Do you t-stats require a com wire and do you have the com going to the SR control? Because of the draw of all three t-stats you may require an external transformer. The 15va transformer on the control may not be enough. Attached is a wiring diagram to add an external transformer to your SR504-4. You can always call into Technical Services during normal business hours Mon-Fri 8am-5pm EST 401-942-8000 and just ask for Technical Services1
-
The zone who does not make the relay noise has the thermostat with his own C and power.
The zone who makes the most noise has the thermostat C from the Taco SR control and has also a Two way zone valve (who uses the transformer on the control) before the pump.
So I think an external power source for all the thermostats might be the answer:
https://www.amazon.com/gp/product/B07DJ7RHS5/ref=ppx_yo_dt_b_asin_title_o00_s00?ie=UTF8&psc=1
I will let you know. Thanks1 -
What type of zone valve do you have? I have wiring diagrams for our heat motor ( 3 wires ) and zone sentry ( 4 wires ) when connecting to an SR control.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements