Retrofit Hydronic Infloor heating to existing slab, polished concrete
lummock
Member Posts: 3
I have a 100 year old home with cast iron radiators throughout, located in Northern Ontario Canada.
It is comfortable and reasonably easy to heat, despite temperatures being cold in the winter.
I am in the process gutting and refinishing the 70’s finished basement.
It is comfortable and reasonably easy to heat, despite temperatures being cold in the winter.
I am in the process gutting and refinishing the 70’s finished basement.
Part of this process will involve moving from a mid efficiency boiler to a condensing combiboiler for space savings, and efficiency, I have read plenty of horror stories on combis, but I will persist as we don’t have the space for a tank.
The prior owner had built cast iron radiators, on their own zone, INTO the 2x4 walls which were insulated with fibreglass bats. This was probably not ideal from a heat transmission perspective, and will not be part of the new plan.
I assume the slab is uninsulated.
I would like to add a heated polished concrete, or gypcrete /epoxy, floor, roughly 1000 sq feet and remove all the cast iron radiators.
I assume the slab is uninsulated.
I would like to add a heated polished concrete, or gypcrete /epoxy, floor, roughly 1000 sq feet and remove all the cast iron radiators.
How much headroom would i give up to achieve this? Currently the floor is just vinyl tiles glued directly to the concrete slab, and is cool underfoot summer and winter.
I have looked a lots of products such as warmboard,Roth panels etc, but Im still a bit unsure if any of them are a smart idea.
I have read about perimeter insulation and disconnecting the slab, but am unsure the value or how to achieve this.
The walls and rim joists will all be sprayfoamed.
Though I will be jackhammering sections of the floor to move toilets I’m not keen on doing the whole floor in order to add 2” of rigid insulation and repouring my slab. I’m also not sure if this would damage the house.
I appreciate any suggestions as to if this is a non starter or if this can be done.
This is not a house I plan on flipping, it will done right or not at all.
If there are suggestions please include the rough finished height as well as the order of materials, it’s hard to picture how much headroom I’ll lose.
I could be convinced to move away from radiant floors, and polished concrete, but if so I would also like something to insulate the slab as the floor is cold as it stands.
thanks in advance
I have read about perimeter insulation and disconnecting the slab, but am unsure the value or how to achieve this.
The walls and rim joists will all be sprayfoamed.
Though I will be jackhammering sections of the floor to move toilets I’m not keen on doing the whole floor in order to add 2” of rigid insulation and repouring my slab. I’m also not sure if this would damage the house.
I appreciate any suggestions as to if this is a non starter or if this can be done.
This is not a house I plan on flipping, it will done right or not at all.
If there are suggestions please include the rough finished height as well as the order of materials, it’s hard to picture how much headroom I’ll lose.
I could be convinced to move away from radiant floors, and polished concrete, but if so I would also like something to insulate the slab as the floor is cold as it stands.
thanks in advance
0
Comments
-
It will come down to how much heat energy you want to give up to the ground below
2” under slab insulation is common these days, plus slab get you up into your headroom a bit. Stairs would need to be reworked
So those are the trade offs. Radiant ceiling s good second optionBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I believe a product like Warmboard would have some insulation value to thermally uncouple from the slab below. It also has the aluminum surface on top to conduct heat to whatever finished floor material you'd use. The floor height it would add is the least you could practically expect to gain. But it does not come at a low price-point. Hot rod's radiant ceiling is a good alternative (the next best) to radiant floor. You MUST insulate above the radiant tubing.
0 -
Can you put fiber reinforced concrete or gypcrete over Roth panels or warm board?If so what is the minimum recommended thickness?0
-
I suppose you could. But...you'd better ask Warmboard tech support. They'll certainly have an opinion. I found them to be very helpful.0
-
If you are imbedding the tubes in concrete, you really don’t need warmboard.lummock said:Can you put fiber reinforced concrete or gypcrete over Roth panels or warm board?
If so what is the minimum recommended thickness?
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Then, where does the thermal isolation from the old slab happen?0
-
lummock said:Can you put fiber reinforced concrete or gypcrete over Roth panels or warm board?If so what is the minimum recommended thickness?If you use a pea gravel concrete mix3/8” aggregate you could get down to a thin pour. As I recall 3 times the stone size over the tube
Expect “road map” type cracking on a thin slab. The fibers in the mix make it hard to get a mirror finish unless you power trowel
which melts off the exposed fiber.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
psb75 said:Then, where does the thermal isolation from the old slab happen?Obviously in an ideal world 2” eps and 4” concrete is the solution.
Hotrod, can you elaborate on what you mean by a proper trowel, it sounds like something heated.
I hadn’t thought of problem of aluminum over concrete would it flex or crack more easily
thanks again for you comments0 -
I think the lime in the concrete may attack the aluminum? Maybe once it cures it would be fine?
Power trowels burn off those polypro fibers from the friction. And, properly operated< get you the most polished finish. Electric versions for indoors. On the large commercial slabs they have ride on versions.
Rigid foamboard like Dow is the best for under concrete, it's rated for that use. My thought would be 1" minimum, R-5. Anything thinner tends to crack and break when you work with it. With the pre-made over the slab products, it's the thickness under the tube where the heat loss occurs and insulation is thinnest. I like the Roth panel, but maybe 1/4" of foam under the tube.
I'd rather the tube on a solid 1". but it is the " tradeoff.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I thought Warmboard had a version with insulation underneath it. It doesn't. Roth panels do. Their 1/2" panel has R 4.5. That's the most they offer. Most of these radiant panel systems are designed for most flooring products: hardwood, tile etc. If you want something approaching the performance of concrete (i.e. more thermal mass) use Hardiboard and tile. Not quite the same mass as 4" concrete but more than wood.0
-
I've alway been told about the best you can get from any foam is R-5 per inch. So I',m not sure how a 5/8" thick foam panel gets 4.5? Also below the tube is certainly not R-4.5? A bit of a sales spiel, unless the aluminum add r value
I do like the Roth panel system, I have always used them over wood sub-flooring, glued and stapled down.
I'd choose this over WB for over concrete and I like the 6" OC of the Roth better. The tight spacing and solid aluminum allows for the lowest SWT.
WB is nice if you are nailing over it, it holds nails well.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements